It's not just megger I find but others I've used can be so inaccurate. Get one reading then immediately press the test button again and get a completely different one!...

Instead I've started getting the apprentice to hold a pocket calculator up while I throw my screwdriver at him five times. I then use the number on screen.

Its also quicker that way!...
 
The No trip test uses a smaller current over a longer period, than the Hi test. This will useually give a higher reading. Also, the voltage will fluctuate slightley and this may also affect the result.
 
The No trip test uses a smaller current over a longer period, than the Hi test. This will useually give a higher reading. Also, the voltage will fluctuate slightley and this may also affect the result.

turn the right hand knob to the spanner and the left hand knob to V
it will them display the firmware version
 
ive had a similar problem with my megger MFT1552 where I had a length of 2.5 twin and earth as a radial 3m from the mains one socket one cable got a reading of 0.98 ohms thought either corroded connection or loose conductor but not to be tested loop at mains to be 0.14 ohms very strange disconnected the RCD and got 0.23 have found since my tester does not like the new Mk sentry RCDS and they seem to add high resistance to the reading aot more than the actual value do not find this problem with starbreaker or hager
 
ive had a similar problem with my megger MFT1552 where I had a length of 2.5 twin and earth as a radial 3m from the mains one socket one cable got a reading of 0.98 ohms thought either corroded connection or loose conductor but not to be tested loop at mains to be 0.14 ohms very strange disconnected the RCD and got 0.23 have found since my tester does not like the new Mk sentry RCDS and they seem to add high resistance to the reading aot more than the actual value do not find this problem with starbreaker or hager

I only use MK if I need a left hand side main switch, the last two I have fitted have all added about 0.6 to any expected Zs measurements. Both times I had done Zs and R1R2 readings prior to changing the board and then got totally different readings on Zs after the event.

Rubbish.....
 
thought it was me but Mk have really fitted cheap nasty nits in their boards now and the RCDS are not compatible with trip lock loop tester readings total ********
 
Yes I've found on the Megger LTW model no trip gives so massively inaccurate results at times.
Seems worse the higher the earth loop would naturally be almost like it exaggerates the readings
 
Does anyone have issues with this test and how accurate is a No trip test?

I find my readings seem to change a fair bit testing the same circuit a few times.

This is using a 1730.
You have to remember that the MFT is only injective 15mA into the earth on the no trip so that the RCD will hold and on the HI current loop it injects 25A which will give you a more accurate reading. Some of the RCD do cause issues so if you are not happy with your results link the CPC and Line conductors out at the far end of the circuit and test on high at the CU without it going through the RCD on the isolated circuit! I have had a few issues when testing Europa and BG RCD on the no trip with a 1552 and a stand alone loop tester ! You should have a good idea what your EFLI result should be from you dead tests IMO!
 

Reply to ELI on no trip with Megger MFT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
578
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
308
Hi I've got a megger mft 1720 that I was hoping any one can shed any light on When performing continuity tests (even when nulling the leads)...
Replies
13
Views
2K
I've just been to a job to replace a burned out switch where the customer supplied his own Arlec dimmer switch. During a dull moment, I read the...
Replies
6
Views
719
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock