In a standard set up for emergency (non maintained) lighting ,in an HMO for example, is it necessary for the lighting to form a single circuit i.e to be simultaneously isolatable for testing purposes or can each light be fed separately with its own test switch?
 
Nowadays you can get emergency lights with a test switch built in. Also Cosnic do emergency control gear with built in self test. But one switch to bind them all is ok, the only problem being is you can't see the lights on other floors when you use one switch. So quite often it is one switch per floor.
 
You can have one test facility or individual. The main criteria is that non maintained fittings operate upon failure of the associated general lighting circuit. For example if you have a non maintained fitting in a corridor it must illuminate upon failure of the general lighting in that corridor.
 
Nowadays you can get emergency lights with a test switch built in. Also Cosnic do emergency control gear with built in self test. But one switch to bind them all is ok, the only problem being is you can't see the lights on other floors when you use one switch. So quite often it is one switch per floor.

Apols for laziness but do you know who makes them?
 
Who is going to do the monthly test? In the flats I look after, the maintenance man does the monthly test. I think he wouldnt be too amused at having to drag a pair of steps all over 5 blocks of flats and turn off multiple test switches.
One switch off, check they work, sign the book and move on.

Any faults and the annual 3 hour tests are done by yours truly.
 

Reply to Emergency lighting BS 5266 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
637
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
607
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
829
Hi all can a Maintained emergency exit bulk head light fed from non lighting circuit if it is correctly fused and test point provided if no...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock