Hi, does anyone know what you would put in the boxes on page 2 of the EL PIR the section I am referring to is part I - categories of operation.
I have seen a completed cert and these boxes seem to have X's and O's in the boxes what do these mean???
 
7.10 Categories of operation of emergency lighting systems
/
Categories of operation are specified in BS EN 50172:2004/BS 5266-8:2004, 5.6.
/
In this standard, emergency lighting systems are classified according to the following parameters, as given for luminaires in BS EN 60598-2-22:1999, Annex B:
/
a) Type:
X self-contained;
Y central supply;
/
b) Mode of operation:
0 non-maintained;
1 maintained;
2 combined non-maintained;
3 combined maintained;
4 compound non-maintained;
5 compound maintained;
6 satellite;
/
c) Facilities:
A including test device;
B including remote rest mode;
C including inhibiting mode;
D high risk task area luminaire;
/
d) Duration of emergency mode (in minutes) for a self-contained system:
10 to indicate 10 min duration;
60.............1 h duration;
120............2 h duration;
180............3 h duration.
Previously, emergency lighting systems were categorized by the prefix “M” for maintained and “NM” for non-maintained systems, followed by an “/” and the number of hours duration claimed for the installation, e.g. for self-contained systems:

M/1 was a maintained 1 h duration system; this is now [X][1][****][60]

NM/3 was a non-maintained 3 h duration system; this is now [X][0][****][180]
/
NOTE **** in the third box stands for the facilities [see item c)], details of which are added, as applicable, at the time of installation.
 
Last edited by a moderator:

Reply to emergency lighting PIR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi. I'm an I.T.. engineer with some outdated electrical experience. I qualified C&G 2330 17th edition about 15 years ago, but my only experience...
Replies
4
Views
775
Gents, What is your view from this this clause from BS5266? If you have a lobby with that is part of an escape route that has one fitting, I...
Replies
5
Views
755
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
484
Hi So I'd like a maintained emergency light but without the automatic emergency function to trigger in the event of power failure. In other words...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock