Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Emergency power cut switch in the Electrical Tools and Products area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Rolf Hayes
    Offline

    Rolf Hayes EF Member

    We have a battery operated device that needs to operate when there is a power cut, in effect like an emergency light fitting would.

    Can any one help with a switch that will be triggered when power to the property is lost so that the battery operated device will run the frost protection device. Have thought about rigging up a bit of a homemade setup with a relay and just have the battery wired through NC so that the relay will be on all the time there is power to the property.
     
  2. Shoei
    Offline

    Shoei Regular EF Member

    Location:
    nantwich
    The question needs more information, what voltage, how much power how long should it hold up for? The usual solution would be a UPS.
     
    • Agree Agree x 2
  3. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    Do you have a lot of power cuts in the winter then? What are you protecting from frost plants?
     
  4. Rolf Hayes
    Offline

    Rolf Hayes EF Member

    Thank you Shoei

    The voltage and power would only need to be sufficient for a low voltage trace heating, so something like 24v for a trace heating of 10W/m, a total length of 15m.

    A UPS system was concidered but thought to be too much for what is required.

    It is expected to hold out only when it is below 5 degrees outside (was going to have a mechanical frost stat for this) and when there is a power cut.

    Trust this helps and grateful of your help.
     
  5. Rolf Hayes
    Offline

    Rolf Hayes EF Member

    We are needing a contingency in place for some external pipework to a heat pump where we haven't been able to add glycol or antifreeze to the system.

    I have to agree that power cuts at the same time as a cold winter for long enough to freeze water that has been at 30 degrees is almost unheard of but the client is adamant that the protection is needed.
     
  6. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    So this trace heating is only required during power cuts to prevent the stationary liquid freezing?
    Surely the best way is a UPS with 230v output to a power supply with the 24v output. Batteries do not seem a good idea as you will have to have some charging facility for them.
     
    • Agree Agree x 1
  7. Shoei
    Offline

    Shoei Regular EF Member

    Location:
    nantwich
    Have you identified the float charger and battery? If the charger has a charge status signal it could be used to operate a relay which connects the heater. If there's no charge signal, a diode and relay could be used to do the same thing.
     
  8. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    Is the frost protection intended to be dual fed, or is just intended to be used during power cuts and fed from the battery?
     
  9. Rolf Hayes
    Offline

    Rolf Hayes EF Member

    Frost protection is only to be fed during power cuts.
     
  10. rapparee
    Offline

    rapparee Electrician's Arms

    Location:
    Ireland
    You know we used to make heat pumps and we always had antifreeze in the system, are you sure this won't be possible?
     
  11. Rolf Hayes
    Offline

    Rolf Hayes EF Member

    We aren't able to put antifreeze in as some of the fittings and materials used contain a rubber that can be degraded with propylene glycol and we aren't able to add ethylene glycol as is has potential to come in contact with the hot water cylinder coil, being against regulations and health/safty standards.
     
    • Informative Informative x 1
Loading...
Similar Threads - Emergency power switch Forum Date
Hospital 'emergency' Zs when on back-up generator Electrical Wiring, Theories and Regulations Jan 12, 2019
Trainee Emergency lighting for a beginner Lighting Forum Dec 28, 2018

Share This Page

Users found this page by searching for:

  1. power cut switching relay

    ,
  2. electrical switch to cut power

Electricians Directory Post a Domestic Job Post a Commercial Job