cprfenom
-
- Reaction score
- 108
Hi Guys,
This is my situation:
Existing brick building demolished and replaced with steel frame, steel panel clad warehouse/storage structure.
Original building had two electrical supplies:
1 x 63A single phase and neutral via 3 core PVC SWA PVC
1 x 100A TPN via 4 core PVC SWA PVC plus equal csa CPC
Both supplies will be reinstated but only SPN used to feed LED lighting, small power, intruder/fire alarm supply and electric roller shutter.
Will be providing RCBO protection on final circuits but is there a get out clause for not providing RCD on alarm circuit?
Existing incoming main is approx. 60 years old comprising an 800A TPN cubicle panel fed from a 750kVA on site transformer.
Cubicle is fitted with BS88 fuse protection to sub main cables feeding various distribution boards throughout the building.
Surge protection class 1/2 will be installed in the new building, but not sure if the client wants to install lightning protection.
I guess my question is to TT or extend the existing TN-S?
This is my situation:
Existing brick building demolished and replaced with steel frame, steel panel clad warehouse/storage structure.
Original building had two electrical supplies:
1 x 63A single phase and neutral via 3 core PVC SWA PVC
1 x 100A TPN via 4 core PVC SWA PVC plus equal csa CPC
Both supplies will be reinstated but only SPN used to feed LED lighting, small power, intruder/fire alarm supply and electric roller shutter.
Will be providing RCBO protection on final circuits but is there a get out clause for not providing RCD on alarm circuit?
Existing incoming main is approx. 60 years old comprising an 800A TPN cubicle panel fed from a 750kVA on site transformer.
Cubicle is fitted with BS88 fuse protection to sub main cables feeding various distribution boards throughout the building.
Surge protection class 1/2 will be installed in the new building, but not sure if the client wants to install lightning protection.
I guess my question is to TT or extend the existing TN-S?