Discuss Extent of testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

conrad

-
Reaction score
31
200 A 3phase cutout bs88 fuses... manweb said they wouldnt connect the installed 95mm tails for the installed 100ma rcd for temporary site ofiices etc this supplies a large 3 phase board that currently supplies a smaller 3 phase board from 100 amp 3 phase mcb... If i installed the last 3 phase board and circuits from there and others installed the rcd, 1st 3 phase board and supply cable to our board would we be required to supply the certification for all etc? May not be very clear the way ive tried to describe... Also the issue with manweb saying they dont connect the tails in to there cutout and thqt we should? Cheers
 
It's up to the dno (manweb in this case) to either connect the customers cables or allow safe access for the customer to connect them ie: connections at the top of the ct chamber not in the head. Search the mocopa agreement there is a section on new connections about what the dno and meter operator is responsible for.
 

Reply to Extent of testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
530
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
843
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock