Thanks for the add. wanting to add an outside light to a house but very limited access and they have only just done up the interior with new carpets etc so don't want to make a huge mess. the only supply near to the location is a spur off the downstairs socket circuit going to a SFCU for a boiler. anything I can do with this supply to get a light up for them? Thanks for any advice offered.
 
come off the incomer of the boiler SFCU into a 5A SFCU for light. this extra SFCU can be used as a switch for the light, or you can fit an additional switch. also a PIR light is an option.
 
As long as the spur from the ring is protected by fcu w/13a fuse at its origin you can feed more points from it.

I'd suggest fitting a fcu at the socket the spur comes from then you can do what was suggested above.

Maybe check Zs at the boiler spur to make sure you are not going to fall outside of max values, although this shouldn't be a problem if existing install is of good quality.
 
Whilst I would agree the above is technically correct, if the spur is definitely only serving the boiler FCU with likely a 3a fuse, then adding a second FCU for a light with a 3a fuse is not going to overload the spur cable. In practice this is no different to a double socket on a spur with two 3a appliances plugged in. That the spur is correctly wired directly off a ring circuit would need to be verified though.
 
You can get some good battery operated external led lights these days, with integral PIR and a key fob for manual override. Depends upon how much light they need I guess.
 

Reply to Exterior light with limited options in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
868
Hi there I need your opinion on this one, I need to fix mat 18sqm (200w). Client instead of one mat bought 2 mats (12sqm)+(6sqm) one thermostat ...
Replies
7
Views
800
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
549
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
I have a staircase about 25 feet long with two recessed lights (one up top, the other at the bottom). Each light is on its own 3-way switch, which...
Replies
2
Views
766

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock