    Just wondering if anyone knows what official building regs state about having to install the above when doing a refurb of house?

    I have had building control officers tell me in the past that fans are required in kitchens bathrooms and utility rooms, but I can't find anything in the building regs (approved document F) which backs this up.

    I have a customer who says he doesn't want them and I have told him he has to have them...anybody help??
     
  2. Paul228
    Offline

    Paul228 There is no spoon

    Location:
    Hull in Yorkshire
    I'd guessing, so don't take this as gospel.
    It use to be that you only had to fit extractor fans in a kitchen or bathroom if they didn't have access to free flowing air. Ie, no outside opening window. They will need an overrun timer if there is no outside window.
    A ducted cooker hood would suffice for a kitchen.
    I'll ask my building inspector friend his views when he's home
     
    • Agree Agree x 1
  3. ruston
    Offline

    ruston Respected Member

    Location:
    Northumberland
    • Informative Informative x 1
    Last edited: May 25, 2017
  4. ruston
    Offline

    ruston Respected Member

    Location:
    Northumberland
    You are about spot on.
     
    • Agree Agree x 1
  5. Paul228
    Offline

    Paul228 There is no spoon

    Location:
    Hull in Yorkshire
    Spot on Ruston.
    Page 40. 7.23.
    Basically if you are doing building works, then you you can't make the ventilation worse ie if it had a fan or cooker hood to the outside then you have to maintain or replace.
    If it didn't, and you have opening Windows, then there is no requirement to fit one.
     
    • Like Like x 1
  6. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    Are building control involved in the project?

    If so the client has too comply!

    If not crack on... But I think they are mad
     
  7. valleybilly
    Offline

    valleybilly Scuber Do

    Location:
    Manchester
    Only used to apply if you are moving the origional bathroom on a full renovation or adding a new one . the origional bathroom dose not need to comply
     
Loading...
Similar Threads - Extractor fans kitchens Forum Date
Fitting bathroom extractor fans DIY Electrical Forum Dec 31, 2018
Extractor fan with pir wiring question DIY Electrical Forum Jan 14, 2019
Thread Status:
Not open for further replies.

Share This Page

Users found this page by searching for:

  1. bathroom extractor fan that doesnt need to be ducted

    ,
  2. building regulations extractor fans utility room

    ,
  3. building regulations utility room

    ,
  4. do old buildings require extractor fans in the kitchen
Electricians Directory Post a Domestic Job Post a Commercial Job