Discuss Extractor Hood Tripping Rcd in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
19
Hi all.
When to a job this moring RCD had tripped, narrowed it down to the kitchen sockets, but found that the RCD stayed on for about 20-30 seconds before tipping out. Unplugged everything, so I thought.
Tested the RCD 1x 37ms - 36ms. 5x 11ms - 13ms. Ramp test 19.6 mA.
Then I realised the extractor hood was plugged in. Unplugged it RCD stayed on.
I then plugged it back in and switched it on, everything worked on it so as I was switching it off the RCD tripped.
So I measured the earth leakage on the hood as soon as I plugged it in . it started off about 2mA then slowly increased upto 20mA when the RCD knocked off. This happened even though the hood was not actually working.
Has anyone come across this before?
Thanks
 
Hi all.
When to a job this moring RCD had tripped, narrowed it down to the kitchen sockets, but found that the RCD stayed on for about 20-30 seconds before tipping out. Unplugged everything, so I thought.
Tested the RCD 1x 37ms - 36ms. 5x 11ms - 13ms. Ramp test 19.6 mA.
Then I realised the extractor hood was plugged in. Unplugged it RCD stayed on.
I then plugged it back in and switched it on, everything worked on it so as I was switching it off the RCD tripped.
So I measured the earth leakage on the hood as soon as I plugged it in . it started off about 2mA then slowly increased upto 20mA when the RCD knocked off. This happened even though the hood was not actually working.
Has anyone come across this before?
Thanks
Have you carried out any tests on the Hood itself IR for example?
 
No. This was a job I wasn't expecting this morning. I was at another when a neighbour asked me to have a look. after finding this I just told her she needed a new hood.
 
IR test the Hood as a matter of urgency could be the reason for RCD tripping
 
The hood is disconnected and she knows not to use it. She is also happy to have a new hood fitted, I just couldn't work out why the mA's would increase especially when it is not even switched on.
 
The hood is disconnected and she knows not to use it. She is also happy to have a new hood fitted, I just couldn't work out why the mA's would increase especially when it is not even switched on.
Fan getting warm expanding shorting out somewhere, lectric is a funny fing you know, did you get the job of supplying a new Hood?
 
I wondered if something on the circuit board might have been causing it?
I told her to get someone to fit, but she said that she wants me to do it. So she is going to have to wait though, too busy at the moment.
 
I wondered if something on the circuit board might have been causing it?
I told her to get someone to fit, but she said that she wants me to do it. So she is going to have to wait though, too busy at the moment.
Well it's not a matter of life or death is it/ cooker hoods my old mum just opened the window bless her.
 
Hi M, I agree with Pete - an ir problem. It maybe in the switch wiring area as some hoods have the sw on the underside close enough to the extracted air flow to get a good greasing over time. If so, it may respond a bit of circuit degreaser/contact cleaner spray (Screwfix 92716). Cheers David.
 

Reply to Extractor Hood Tripping Rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
733
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
424
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock