B755B22B-5C1C-4861-8482-E2CC7EFE6A23.jpeg hi guys,

Could someone please tell me why the ‘insulation’ has failed on this pat test please? I thought over 1MOhm was ok?

The test is on a fan in a dental surgery.

Thanks
 
The requirements for PATests are 1.0 Meg ohm for a Class 1 appliance and 2.0 Meg ohm for a Class II appliance. So if it was Class II it is below the required minimum.
 
Thank you got the quick response.

I haven’t done any PAT testing, does this men that the flex need to be changed or that the fan unit is faulty?

Thanks again
 
Well it could be either you need to narrow it down, the three elements which could be causing it are likely to be plug, cord or the fan unit assuming there are no other parts to it.
 
That could just be a visual check as the insulation test would include all parts together and not a separate check on each. Is it a Class I or Class II fan.
 
I’m not sure, I’m am starting PAT testing training soon so have been given some certificates to look at in advance.

Must be class II if it’s failed with those results?
 
I would assume so but a cautious or experienced person may view the reading as warranting attention for a Class I appliance.
 
As Westward says, if there are exposed metal parts, then they will require an IR test...and obviously if there are none then no test because a) you don't need one, and b) you can't...
Fans in particular, as has been mentioned in these forums before, are awkward beggars to test. How far do you go with "finding" exposed metal parts? If you have to dismantle the cage to find some metal to touch then that is going too far imo...but if you "could" theoretically touch an exposed metal part, say around the middle of the rotor, with a finger but not using any tools, I think it is fair to take the safest route and test it with your probe...why wouldn't you? as I say, fans are often tricky due to their widely ranging types of construction...I'm not a fan.
 
Many desk or standard fans are Class I but the metal parts which are earthed tend to be within the motor housing and not open to touch. A good example of a metal cased Class II appliance could be a DVD player and the IR test should be carried out with the earth bond test lead connected to the casing.
 

Reply to Failed insulation on Fan in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
430
  • Question
I am PAT testing an induction hob. It passes the Earth test, but then fails on the Insulation Test. Item is about 3 years old, no damage to unit...
Replies
2
Views
401
Guys Need some advice please. I was asked last week to investigate a burning smell in a toilet turned out it was an extract fan one of 2 The...
Replies
3
Views
706
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
803
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock