Hi all, another year and another problem with Christmas decorations.
I have a project with a large number of fairy lights - 230v through rectifiers, strapped to a metal grid. I am getting a pretty sizeable earth leakage per frame - around 8-10mA which increases to 15 when wet. The lights are from a high quality manufacturer, ip67 rated and tied on with cable ties. Other than the cable ties being too tight reducing the effectiveness of the insulation is there anything else that could be causing the earth leakage? Would induction have an impact as there's quite a bit of that going on.
I have multiple frames and the earth leakage is very similar frame to frame so it makes me think there is no proper short to ground happening and there is something else i have no knowledge of.
Now my real question is whether this really is an issue, does it need to be covered by an RCD? The location is way out of reach of the public and the 32A outlet could be considered as for specific use, is there anything in the regs that make it so all outside sockets require RCD protection regardless of application? One outlet is feeding two frames and when wet the leakage rises just enough to trip the 30mA RCBO, if you plug one in on its own - no issues.
Any thoughts appreciated.
I have a project with a large number of fairy lights - 230v through rectifiers, strapped to a metal grid. I am getting a pretty sizeable earth leakage per frame - around 8-10mA which increases to 15 when wet. The lights are from a high quality manufacturer, ip67 rated and tied on with cable ties. Other than the cable ties being too tight reducing the effectiveness of the insulation is there anything else that could be causing the earth leakage? Would induction have an impact as there's quite a bit of that going on.
I have multiple frames and the earth leakage is very similar frame to frame so it makes me think there is no proper short to ground happening and there is something else i have no knowledge of.
Now my real question is whether this really is an issue, does it need to be covered by an RCD? The location is way out of reach of the public and the 32A outlet could be considered as for specific use, is there anything in the regs that make it so all outside sockets require RCD protection regardless of application? One outlet is feeding two frames and when wet the leakage rises just enough to trip the 30mA RCBO, if you plug one in on its own - no issues.
Any thoughts appreciated.