Surely when testing for borrowed neutrals you don't test between neutrals? Surely the live of one circuit against neutrals of all other circuits, neutral to neutral shows only interconnection between neutrals
 
Testing between neutrals would work so long as everything is on as there would be a connection through the faulty load and one of the OK loads to give the reading, but from line to another neutral would only be testing through the faulty load so gives a chance for diagnosis.
However if the load is electronic and near infinite resistance it may not show up.

This is my thought:
Shared Neutral Test.jpg
be interested in feedback.
 
Testing between neutrals would work so long as everything is on as there would be a connection through the faulty load and one of the OK loads to give the reading, but from line to another neutral would only be testing through the faulty load so gives a chance for diagnosis.
However if the load is electronic and near infinite resistance it may not show up.


This is my thought:
View attachment 23537
be interested in feedback.

That makes perfect sense to me and the drawing makes it even easier to understand. Thanks mate
 
I would try and trace with earth leakage clamp meter with an MCB in for now, and trace it through with just that 1 circuit live then liven up other circuits and see what happens with the readings , you could try with lamps in first and all switches off , then try with switches on one at a time , trace it that way ,
 
Originally Posted by londonlec
Does the circuit definitely need an RCBO...
Why have you asked this?

Because he wants to know if the circuit needs an Rcbo sorry dillb, couldn't resist
icon10.png
 
Why wouldn't they?

They have a duty of care to ensure everything is safe, if it's tripping find fault repair then all is good.

Had this yesterday, RCBO keeps tripping narrowed it down to faulty light, removed fitting all ok now. RCBO still on circuit and not tripping anymore.
 
rcbo

Try swapping rcbo with a known good one from another circuit. I had a similar problem some time ago spent ages doing all checks and tests turned out to be duff rcbo very annoying had to go home and kick the dog!
 
Re: rcbo

Try swapping rcbo with a known good one from another circuit. I had a similar problem some time ago spent ages doing all checks and tests turned out to be duff rcbo very annoying had to go home and kick the dog!


No need to swap if it was ramped.

Boydy
 
Riiiiight. So I have made a bit of an error. When doing IR test I disconnected cpc neutral and live and did it that way. The cpc wasnt going anywhere, the lights bprrowed the cpc from various local points. Not awful but very rough I know! I had a fun day disconnecting sets of lights bit by bit. Turns out they are pretty much all letting in water. Going back to change 10 lights tomorrow and Monday. Eurgh...

Cant believe i made that IR cock up. I must admit, i have a love hate relationship with IR tests. So many variables to give you low results and the wiring is slapdash in this place to say the least with so many variables I'm not sure where to start!!
 
You're right there. I did learn that somewhere. But it'd been a long day and I wasnt with it.

Now this is odd: All the lights are on when PIR is overrided. When i switch a particular submain (on its own rcbo) one light goes out. Now this HAS to be borrowed neutral surely because switched live is fed from one contactor?! Or perhaps switched live and neutral from different circuit is feb from contactor? I'm a bit baffled. Lights are on mcb til i sort probs out. But rcbo feeding submain does NOT trip which is why borrowed neutral looks v unlikely. Someone help me i feel like i'm losing the plot, not slept much since son was born, i swear having young kids turns your grey matter into cauliflower....
 

Reply to Fault has stumped me!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
411
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock