I have been asked to look at a faulty 12v downlight in a hotel.I have been informed that the following measurements have been noted at the transformer input: L - E 240v,N - E 240v,and N - L 0v any ideas please.
 
Hi,
I have been asked to look at a faulty 12v downlight in a hotel.I have been informed that the following measurements have been noted at the transformer input: L - E 240v,N - E 240v,and N - L 0v any ideas please.
Who noted the measurements:confused:Have you tested it yourself.Could be a faulty transformer.What about the lamp itself.:confused:
 
Trust me this is a broken nutural no dout about it, you are getting a potential differance accross live to earth as live is at 230v and earth is at 0v, a potential differace accros n and earth because the transformer is still connectde and the live goes in the transformer through its winding and out thus making nutural live. you get no pd accross the live and nutural because the nutural has no return path,

regards

Aj:)
 

Reply to faulty downlight in the Australia area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
465
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
354
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
403

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock