Wylex CU, so I guess it must be a Wylex RCBO then.
It's the fridge freezer, I would like it to be on a separate RCBO.
A good plan.
Which scheme are you going to join then?
By the sound of your jobs/posts you are working outside the rules of Part P or are you paying LABC a lot of money?
So from this you would not sensibly be able to fit an RCBO into a CU that was made over ten years ago as they would not have been tested with RCBOs? you would have to change the CU to a more modern one.BS EN 60439-3:1991 as amended 2009, effectively restricts the choice to the manufacturers type tested RCBO and Distribution Board combination. Any deviation from this and the Sparky would become responsible for type testing and certification of the combination he has chosen ... not a viable option IMO.
Reply to Favourite RCBO in the Electrical Tools and Products area at ElectriciansForums.net
Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.