I'm sure we've all come across these scenarios:

16A supply to garage from consumer unit to a socket and an FCU feeding the lights with a 5A BS1362 fuse.

32A ringmain extended to feed conservatory with FCU with 3A BS1362 fuse feeding garden/patio lighting.

Central heating supply from ringmain or dedicated 16A circuit, all controls fed in 1mm PVC-PVC flat cable via FCU with 3A BS1362 fuse.

Now my question is, how do you go about doing the testing and recording the results on a minor works certificate considering the FCU alters the supply characteristics of the final circuit. Do you provide separate R1+R2 and Zs reading for everything after the FCU, do you test to the furthest point on the circuit and record it as if the FCU doesn't exist or do you just test at the FCU as though that is the final point and disregard everything there after. Or, do you do something else entirely?

Would be interested to know what you do.
 
Last edited:
Agree with spin there I would note it as a sub circuit within a circuit and over 2 lines.

Of course if your Ring final is RCD/RCBO protected and the spur is just a normal FCU then really the FCU EFLI for that 1362 fuse is pretty much negated, and would just enter 1667 in the appropiate box. The 3amp 1362 is just there for overload protection on that sub circuit.

If it was the other way round the FCU was RCD protected and the ring final was BS 3036 or MCB protected then I would enter over 2 lines the recorded Zs value for the ring final and then 1667 for the sub circuit.
 

Reply to FCUs as circuit protection for part of circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
772
Hi, quick question. How do FCU's work? Do they just protect the load side and what I mean is, say you have a ring final with 2.5mm^2 protected by...
Replies
9
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K
Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
Replies
35
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock