Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.

Discuss Feeding a Shed Cu from the main CU in the Electrical Forum area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. robbo777
    Offline

    robbo777 Regular EF Member

    Hi I am putting a Small 2 way CU in a shed to feed 3 x double sockets and 2 x florescent lights. The run from the Main CU is 30m

    I am wiring it in conduit and I will be using 4mm singles to supply it with a 20A Breaker at the main, is this ok?

    Many Thanks
     
  2. telectrix
    Online

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    looks good to me. i assume you are taking your cpc for the shed from the MET. if using steel conduit, it should be earthed.
     
  3. robbo777
    Offline

    robbo777 Regular EF Member

    Hi

    The conduit is plastic and yes I'll be taking the CPC from the MET, many thanks
     
  4. Knobhead
    Offline

    Knobhead Guest

    How/where will the plastic conduit be run?
     
  5. robbo777
    Offline

    robbo777 Regular EF Member

    The conduit runs around the external of the building already feeding 4 outside lights at approx 2.5m high, at the end of the run I have brought the conduit down to ground level where I will have an external Junction box, from this box I will be running SWA underground then to the CU in the shed
     
    Last edited: Feb 15, 2012
  6. telectrix
    Online

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    make sure the armour of the SWA is earthed at the house end.
     
    • Like Like x 1
  7. robbo777
    Offline

    robbo777 Regular EF Member

    Just had a though about this, I was planning to put a 2 way CU in the shed with an RCD but just remembered that I can't have an RCD in the shed unless the main RCD is time delayed.
    Shall I split the tails and have the shed on its own supply or shall i not worry about the shed RCD and just rely on the main?

    many thanks
     
  8. tonycoysh
    Offline

    tonycoysh Guest

    Personally I would be splitting the tails or feeding it from your CU with a dedicated RCBO (depending on type and room within CU) , 3 dbl sockets in a shed sounds like your intending to do a bit of work in there. The regs do suggest segregation of circuits should be considered to minimise downtime and inconvenience through fault. Just imagine Mrs or Junior robbo777 are doing some work on the PC when you cut through the lawn mower cable and they loose it all because the RCD in the house trips.

    As for time delaying an RCD any s/o etc it protects must still be rated at 30mA in .4s so time delay the one in the house a then circuits within the house aren't protected in a satisfactory way.

    Although if you split the tails I think I'd be wanting to run swa from the split to the db in the shed. Unless you use a 63A RCCB at the split, then you could get away without SWA all the way. But if it were me and I was going to the effort of splitting I think I would want the RCD in the shed so I didn't have to wonder into the house to reset in the event that there was a fault. In which case I think I would use SWA from the split.

    Having said all of that my outside socket is protected by a shared RCD in the house but then junior is only 1 and Mrs mainly uses a Laptop so I am fairly safe. As long as the TV stays on :shocked3:

    Hopefully makes sense and helps a little, I'm sure some of the more time served guys on here can advise us both better :D
     
  9. Engineer54
    Offline

    Engineer54 Guest


    Why would after splitting the mains, and installing a 100mA S type RCD to the tails to the shed, affect THE 30mA RCD's in the CU??
     
  10. tonycoysh
    Offline

    tonycoysh Guest

    Sorry my bad, didn't make myself clear enough, I was replying to thisparticular comment.

    Assuming the tails were not split and the 2nd db was fed from and RCD protected CB in the house CU the house RCD couldn't be time delayed and satisfy the other circuits it protects in within the house. Is what I was trying say. Am I correct in thinking this?
     
    • Like Like x 1
  11. SimpleSimon
    Offline

    SimpleSimon Guest

    Location:
    Yateley
    You are right because as you say all other RCD circuits in the house would not meet the correct disconnection times. 0.4s with a time delay on front of it.

    Sent from my GT-I9100 using Tapatalk
     
  12. robbo777
    Offline

    robbo777 Regular EF Member

    Hi

    This setup is in some stables, and the shed that I refer to is acutally a 20 foot lorry back and my dad has a little woodworking setup in there. he only has a few small tools and obviously will only be using one at a time.
    in the tac room where the main CU is, there is only 1 socket and all this has on it is the kettle. there are only people there during the day and rarely have the stable lights on so I wouldn't be worried about nuisance tripping
     
  13. Dannyspark
    Offline

    Dannyspark Active EF Member

    Location:
    Wiltshire
    I may be missing something here so please point it out if I am, but aren't you overly complicating things?

    From what you have said you already have RCD protection in the main CU. Then why don't you just run off of a 20A (2.5mm circuit) or 32A (4mm circuit) breaker covered by this RCD? You should still mechanically protect the cables with conduit or alternatively run the whole thing in SWA right up to the shed.

    You could then fuse down with a switched FCU for your lighting circuit. If you are worried about the lights going out then fit an emergency light (with battery back-up) over the shed door.

    You will have the segregation issue in the house but you can swap circuits around within the CU to ensure minimal disruption in the event of a trip.
     
  14. robbo777
    Offline

    robbo777 Regular EF Member

    I probably am over complicating this a bit but I intend on using this job as my NIC major as I have rewired the whole of the stables and lit the minage and powered the static caravan there too and I just want to make sure I get it all exactly right,
    I really appreciate the comments and help so thank you.
     
  15. Guitarist
    Offline

    Guitarist Electrician's Arms

    Location:
    Norfolk
    I take it that you don't have a load of steelwork in contact with the ground (it being a former 20ft lorry back) ?
     
Loading...
Similar Threads - Feeding Shed main Forum Date
Some advice: Power to a shed Electrical Forum Jan 8, 2019
Does the brushed DC motor and Permanent magnet Dc motor need position feedback in the control system Electrical Forum Dec 23, 2018
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job