Referring to pages 158-159 in the OSG
Table 8A
Type, OPD(A)
A1 Ring, 30 or 32 .......etc
8.2.3 Conductor size
....The as-installed current-carrying capacity Iz so calculated must not be less than:
20 A for ring circuit A1
Am I reading/interpreting this correctly when I say that the OSG is telling us you can have a RFC made up of cable with a capacity of 20A and an OCPD of 32A?
Table 8A
Type, OPD(A)
A1 Ring, 30 or 32 .......etc
8.2.3 Conductor size
....The as-installed current-carrying capacity Iz so calculated must not be less than:
20 A for ring circuit A1
Am I reading/interpreting this correctly when I say that the OSG is telling us you can have a RFC made up of cable with a capacity of 20A and an OCPD of 32A?