At the moment this block of 9 flats has a Twin Wire system with communal areas wired and one detector in each flat . I have been asked the possibility of fitting a addressable type system but using the same cables. This is to identify the flat where the alarm has triggered.
The addressable system I have looked at uses loop wiring so not sure if a radial circuit would work.
Has anyone had experience with these systems or can recommend a suitable system.
 
Addressable systems should be able to be wired any which way you want.
I believe you will have to change the smoke heads, etc. for addressable items.
 
How many devices on each leg as we had about 15 on a radial only as a temporary until they could go on the new loop. I take it you can not run a return leg back.
 
Yes you can run a leg back.
Many systems will allow up to 30 items per loop or zone.
The idea of running a loop, is that if one leg fails, then the other leg will still carry signals.
Programmable systems allow you to identify each item, so you could for instance program a smoke head as being male toilets ground floor, or stair well 2 first floor. This can be really helpful, if you have voids which require smoke heads.
 
Thanks for the helpfull replies. There are 12 detectors- which would changed to the addressable type, as it is a posh bock of flats running a new return back would be difficult - just wondering if it would work without the return leg- or do we just bridge it out, not sure how they monitor the loop. Any suggestions on a addressable system which can be installed without buying windows software to set it up.
 
Thanks all for the help I have contacted a specialist company to supply and commission. It looks like a return leg will be necessary.
 

Reply to Fire alarm wiring -Twin wire converted to addressable system in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock