Discuss Fire alarms non rcd protected? 25 characters in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

magnoliafan89

-
Esteemed
Arms
Reaction score
540
Hi guys

Im curious as to how people wire in smoke and heat alarms in a domestic setting. I know you're allowed to put them with a regularly used lighting circuit or on their own circuit...but....does the circuit that has the alarms on need to be non rcd protected? Or is it a case of it they have batteries can they be rcd protected but before the rcd if they arent backed up by batteries?
The company i work for i mostly do industrial and commercial and we wire the smokes in fp200 back to a fire panel which is obviously backed up by batteries but everything in yhe panel board supplying that is rcbo. How does it work in the domestic setting?


Cheers guys
 
I dont understand what the 230 volt has to do with it? Surely in a domestic dwelling the alarms would be 230 on a lighting circuit or not?
Well id assume the cables would be run through cielings and under floorboards
 
Last edited:
If the installation method requires additional protection, then the low voltage cabling would have to have RCD protection.

Think what Buzz is if the cabling for said circuits is extra low voltage, it would not?
 
[QUOTE="magnoliafan89, post: 1381530, member: 98919]
Well id assume the cables would be run through cielings and under floorboards[/QUOTE]

If it’s a house they have to go up the walls at some point!

Seen this recently in some new builds _ no RCD protection for cooker, smokes or immersion .....whether they should be is something that only the installer could confirm BUT any EICRs in the future would give them a C3 ....

IMHO they should be on RCDs or RCBO’s
 
@magnoliafan89
Can you clarify what you are talking about here. Your title says FIRE alarms, your text talks about smaoke and heat alarms in a domestic environment.
Obviously the requirements are different. (well, to me it is obvious - and I hope it is to you!)
 
For domestic.
If the alarms are interlinked, they should be mains powered with individual batteries in each alarm. The batteries can be replaceable or rechargeable, depends on the alarm.

Mains power can come from a separate circuit or (I think better) from a regularly used lighting circuit. The latter option makes it more obvious if there has been a power failure.

There's no reg about if the suppy circuit is or isnt on an RCD/RCBO but the latest BS7671 (and the new 18th edition) will make non-rcd circuits increasingly hard to come by.

Domestic heat/smoke alarms do not need the similar rigorous installation requirements needed for fire alarm systems. Standard T&E cable is used and not FP200, etc.
 
So long as they are taken from a lighting circuit that is often used then an RCD can be installed. The point being that the homeowner will know very quickly that the circuit is off and it will be in their interest to sort due to the inconvienience.
 
Most smokes will complain at you if the mains voltage, or if the battery dies.
Not too many householders spend time staring at their alarm to check that the power light is on and the operating lights flashes every 30 seconds. .
 
Not necessarily.

Let’s see, cabling in ceilings and floors. Use service riser for cables between floors.
Sorted, no RCD needed on circuit. Regs compliant.
 
Surely you don't document the route of all of the cables in a domestic setting? Just the certificate that says it complies with BS7671 is enough!
 

Reply to Fire alarms non rcd protected? 25 characters in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Daughter has bought a house and it has a home security system, G-Tag setup. Issue is the alarm panel displays are pixelated and you cant see...
Replies
0
Views
647
I'm about to order this wired smoke alarm system as it can network but I just went to see how my existing fire alarms are hooked up and there...
Replies
12
Views
1K
The big stately home I’ve been working in has an EMS 5096 alarm system with over 100 detectors and 3 (that I know of) panels. All detectors are...
Replies
19
Views
945
Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
580
I'm about to start first fixing this fire alarm in the industrial unit we are wiring, at the moment its totally empty and eventually will have a...
Replies
5
Views
841

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock