Not sure if the image will come through properly so its ledgible but here goes, my first attempt at designing my own control circuit, its basically just controls a pump that is going to be feeding biocide into a tank once every 5 hrs, bearing in mind this is just the control side of it and there are still a few modifications to be made, first thoughts? constructive criticism welcome :smiley2:.




Uploaded with ImageShack.us
 

Attachments

  • Proj 1. CL Bio.jpg
    12.7 KB · Views: 143
Last edited by a moderator:
The overloads show as a fault but aren’t in the motor contactor line (2KM5).
I would also find a way of cancelling the alarm sounder. There’s nothing worse than trying to find a fault with a sounder screeching in your ear.
Other than that, well dome.
 
first off at first glance what is controlling the liquid level relay as it it energised all the time, it should have contacts for level sensor. Pump motor contactor needs OL in series.

Beat me again Tony

Just thought do you want a manual overide and emergency stop function??
 
The overloads show as a fault but aren’t in the motor contactor line (2KM5).
I would also find a way of cancelling the alarm sounder. There’s nothing worse than trying to find a fault with a sounder screeching in your ear.
Other than that, well dome.

I thought someone might mention about the overload lol, thats going on the power section page, and the OL auxilliary on this page will refrence back to the OL on the power section :p. '2S2' is going to be a keyswitch for maintenence personnel, (i know it needs a better suited symbol) lol, when switched off will turn the beacon /sounder off but leave a red Indicator on the front of the panel on for the purpose of not ****ing people off haha,

my mistake with '2S1' is meant to be labelled as '2S2'! sorry for confusion and thanks for reply :).
 
Made a few corrections to the original drawing, recon ive got it nearly cracked from the control point of view, thanks for the comments so far, if there is anything else dont hesitate to throw it at me :p .
 
first off at first glance what is controlling the liquid level relay as it it energised all the time, it should have contacts for level sensor. Pump motor contactor needs OL in series.

Beat me again Tony

Just thought do you want a manual overide and emergency stop function??

thanks for the e-stop reminder, couldve been ugly biocide spraying everywhere and no emergency switch lol!
 
2k3 is still constantly energised and there's no wire numbers,which would annoy me no end unless your using marked multicores,which IMO should still be labelled on the diagram.
Aside from that and the above a lovely diagram,I'd be able to fault find with that no worries.
 
A nice clear, easy to follow drawing although I prefer to see wire numbers as well. Most of the plant I work on is built in Germany and does not have wire numbers just terminal to terminal. If you're going to get seriously into design/drawing have a look at eplan, a very powerful bit of kit!.
 

Reply to First attempt at a v.small control circuit design, /w image. in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
Hi all, Some background on this question: I am UK-based, and I work with robotics and automation, so have experience with PLC programming, robot...
Replies
0
Views
918
Hi Guys and Girls, First off: I am very new to electrical stuff. Right now I'm running my first ever project containing electrical components. So...
Replies
2
Views
1K
Hi, I've got both a solar pv and an ashp system. The solar system also has 2 batteries and it's configured to fill the batteries first and then...
Replies
0
Views
1K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock