Had a call, the lady had no power in her property.

Turn main switch off remove cover and test at incoming side of switch 230V.
Turn main switch on and at the other side of the main switch 50V. Faulty main switch I thought.
Turn off all RCD's and MCB's and have 230V where I found 50V previously. Turn RCD on and each MCB individually and when under load there is only 50V. L-E I have 230V at all times.

I could only think that there is a loose neutral and being underload losing the voltage?
 
Sounds like a missing supply neutral and your first test on the incoming side was made using a digital tester with an astronomically high input impedance. If you redo the first test with an analogue tester you probably won't see anything close to 230v.
 
Did you fix this or is the Power still OFF.?


under load there is only 50V. L-E I have 230V at all times.

I could only think that there is a loose neutral and being underload losing the voltage?

Can't possibly be the Neutral, you're not testing with it.

With all MCB / RCD turned on if you have 230 L-N and 230 L-E on the incoming to the main switch AND 50v L -E on outgoing side, it can only be the mainswitch failed on L.
 
Yes I'd say it was a supply fault. Seen a similar fault on a 3 phase supply. Tested all good with main switch off, as soon as it was switched on and under load one of the phases dropped out. They were digging up the road after that.
 
Not sure what has gone on I haven't been called back, it's a contract we have with social housing. Make safe and leave unless it can be fixed in an hour or so. Phoned the social housing and said it was a supply issue haven't heard back, they have arrangements for this she's probably in a void property newly refurbished, loving life

As far as tests go. (Kewtech 65) Main switch off Z(impedance) L-PE fine L-N fine. Main switch on (under load) no power and can't test
 
Did you fix this or is the Power still OFF.?


under load there is only 50V. L-E I have 230V at all times.

I could only think that there is a loose neutral and being underload losing the voltage?

Can't possibly be the Neutral, you're not testing with it.

With all MCB / RCD turned on if you have 230 L-N and 230 L-E on the incoming to the main switch AND 50v L -E on outgoing side, it can only be the mainswitch failed on L.

50V. (Full stop & new sentence) L-E I have 230v at all times.

Read the bleeding post 3 times before replying those are the rules!!:p
 

Reply to First time I've come across this fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock