Hi guys,
So i've ditched my 20 year old tricity bendix cooker. Bought a new hob and a single oven and am currently in the process of getting them fitted.
I currently have a dedicated cooker circuit, 32a and 6mm. Switch above the worktop and 2 outlets running off it, a hard wired one and a plug (presuming the plug is for the spark on gas cookers only?) anyway... I have bought a induction hob which runs on full whack at 6500w and in its manual it says its rated at 7.2kw, 28.1a. (whirlpool ACM822NE)
So i assume this can go hard wired in all AOK.
The single oven ive bought is 2.16kw (matrix ms002ss)
I've called a handful of sparkies, and ive got quotes for fitting from £30 to £200.
Around 50% of those i called said both will run fine off the same 32a dedicated cooker cirtuit. While the other 50% either said i need to upgrade the 6mm to 10mm, or add a extra spur for the oven. Lots of random different information i've received.
My old cooker i had for 20 years total KW was 11kw and something like 10,000 watts. I regularly had it on full blast ie... 4 rings and oven (not grill) and i never had any problems with tripping..etc.
Advice much appreciated.
So i've ditched my 20 year old tricity bendix cooker. Bought a new hob and a single oven and am currently in the process of getting them fitted.
I currently have a dedicated cooker circuit, 32a and 6mm. Switch above the worktop and 2 outlets running off it, a hard wired one and a plug (presuming the plug is for the spark on gas cookers only?) anyway... I have bought a induction hob which runs on full whack at 6500w and in its manual it says its rated at 7.2kw, 28.1a. (whirlpool ACM822NE)
So i assume this can go hard wired in all AOK.
The single oven ive bought is 2.16kw (matrix ms002ss)
I've called a handful of sparkies, and ive got quotes for fitting from £30 to £200.
Around 50% of those i called said both will run fine off the same 32a dedicated cooker cirtuit. While the other 50% either said i need to upgrade the 6mm to 10mm, or add a extra spur for the oven. Lots of random different information i've received.
My old cooker i had for 20 years total KW was 11kw and something like 10,000 watts. I regularly had it on full blast ie... 4 rings and oven (not grill) and i never had any problems with tripping..etc.
Advice much appreciated.