Hi, called to a job where the "lights flicker"
Old rewieable fuse board with no RCD 5A light circuit which does flicker randomly every 20>30 seconds or so, no other real loads on .

Stripped the light circuit and found the first light on the loop in system , connected this back up and left the rest disconnected and still the same .
I then removed all other fuses to ensure no other circuit had an effect , still the same.
Finally I rechecked all connections / tightness and plugged a lamp in to a socket directly below the board , with nothing else connected and the lamp still flickered.

I feel it's a external influence but have no specialist test equipment to monitor , could any body throw some light ( non flickering ) on these types of problems?

Cheers
 
Have you tried a different lamp?

A friend of mine used to live near the transformer and he had this problem regular on only one light fitting as it use to sway on the voltage depending on demand in the area. May be worth asking the neighbors if they have a similar thing happening to them
 
hi thanks for the reply, the whole house flickers, I asked about the neighbours and they have no problems, I put my megger across and it maintained 234v all time but that carries no weight in my minds eye.



Have you tried a different lamp?

A friend of mine used to live near the transformer and he had this problem regular on only one light fitting as it use to sway on the voltage depending on demand in the area. May be worth asking the neighbors if they have a similar thing happening
 
hi thanks for the reply, the whole house flickers, I asked about the neighbours and they have no problems, I put my megger across and it maintained 234v all time but that carries no weight in my minds eye.

If you have checked all the connections maybe worth fitting a voltmeter that reads the voltage constantly for a couple of weeks to see if the voltage fluctuates occasionally.

May also be worth carrying out a IR and R1+R2 test too including on the flex of the fitting.
 
So it's an old wiring system on a three plate ? Single P ? You have 'Pulled the fuses' but of course the fuse normally breaks the Line not the N so have the circuit out the board and I R it and do a r1 and r2 after pulling all the vulnerable out
J
 
Sounds external, Tried isolating it low wattage lamp on the ring ? only had it once before crappy neutral connection in main switch. but it was only the fan across the road in a glass factory kicking in that caused the flickering, sundays it didn't flicker
 
where do you live? if you are in the south we have been having voltage fluctuations that have caused lights to flicker or turn off, but these have eased now.
 

Reply to Flickering light circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
Hi everyone. I live in an older home that still has a few circuits with aluminum wiring. One of these is a lights-only circuit that contains 6...
Replies
3
Views
913
Hi Ive never seen this issue in 35years in the trade and wondered if anybody has any idears. The property is a new build and the installation...
Replies
17
Views
3K
Hi Guys Looking to see if anyone has had the same issues. I went to a tennanted property last year where the house lights were flickering and all...
Replies
4
Views
2K
Hello I have recently moved home and I looking to upgrade lighting across the house to LED. In the kitchen I have found that there is installed...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock