Hi All,

I have just been to a property to fault find a tripping RCD. Lights are flickering. All a bit strange. Vacant property - no loads plugged in. TNCS.

The RCD protects socket circuits, CH, garage etc - but not the lights.

Anyhow, I tested the the RCD - no problem.

I turned off all the breakers for the RCD and turned them back on one at time. Garage circuit tripped the RCD - ah-ha I thought. But then it held. Tried the process again and then the kitchen ring tripped it. Tried again and downstairs ring tripped it. But now all holding. Not so straightforward now....

I tightened up all the connections in the CU and checked roses and switches. Nothing.

Soooooo. I then did something I should have done at the start - and checked the voltage at the tails to the consumer unit.

175 volts.

Just to make sure my kit was OK - went next door -247 volts.

So have called DNO.

The lights flickering I understand - but I am trying to relate this low voltage reading to the RCD.

Any ideas?
Any other advice?
It's a new one for me.....
 
I'll have the same bet (£5 I think) I've had a few times before - loose neutral in a tee-off joint under the pavement.
 
I was not onsite when the DNO turned up but they did phone me up and confirm a problem with the supply, saying voltage was ranging from 170 to 240 or so over time.

They also confirmed a high Ze of about 2 ohms.

I don't know much more than that at this stage but do know that a supply has been 'altered' recently in a house opposite, and that a smart meter has been recently put in. But I am only speculating what may have gone wrong.

I suspect I'll pop back when supply is repaired - just to carry out a few tests at the board - the RCD especially......
 
Nasty things, loose or lost neutrals on main supply.

I remember once there was a neutral fault on a 2 phase supply of a large HMO.
The fault was a bad joint on the DNO cable in the street (ancient PILC).
The underground joint went altogether and the neutral was lost, the fault was only noticed when all the rcbos tripped but not mcbs, so the lights and non rcd circuits still worked....only because one of the lighting circuits turned out to have a N-E dead short on it (no rcd) so when the supply neutral was lost the current found its way along the lighting neutral, across the short and back to earth! So the 1mm cpc back to the DB was carrying all the current and became extremely hot and melted the cable at the DB and and 2 feet back up the wall! Almost a fire!
 

Reply to Flickering lights, tripping RCD and voltage at consumer unit... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K
I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
780

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock