Had a look at a job earlier which is to replace 9 6ft twin fluorescent fittings in a small warehouse.
At the moment there is nearly 20 single 5 ft fittings, all fed from 1 32 amp MCB and on 3 switches. All cabling is in 1.5mm t+e believe it or not run on some cable ladder that runs the full length of the building.
My questions would be, Is it best or good practice to maybe split the switching of the 9 fittings into 3 lots of 3? As there is cable ladder installed, rather than installing conduit, then pulling in singles, would flex be an acceptable wiring method, cable tied to the ladder, then glanded into the light fittings?
If using HF fittings, will I still be required to use the 1.8 multiplier to do the calc for the circuit.
Thanks in advance
At the moment there is nearly 20 single 5 ft fittings, all fed from 1 32 amp MCB and on 3 switches. All cabling is in 1.5mm t+e believe it or not run on some cable ladder that runs the full length of the building.
My questions would be, Is it best or good practice to maybe split the switching of the 9 fittings into 3 lots of 3? As there is cable ladder installed, rather than installing conduit, then pulling in singles, would flex be an acceptable wiring method, cable tied to the ladder, then glanded into the light fittings?