Toystorywoody
Hi,
I've been to a job where a 50A MCB had blown and wouldn't reset. I didn't have a replacement MCB the same size so I used a bit of spare cable rated to 48A in the bs7671 book so that the cable would break and de-active the circuit before 50A is overloaded.
I'm not 100% sure if I made the right move or not, can anyone help?
Thanks in advance.
Woody
I've been to a job where a 50A MCB had blown and wouldn't reset. I didn't have a replacement MCB the same size so I used a bit of spare cable rated to 48A in the bs7671 book so that the cable would break and de-active the circuit before 50A is overloaded.
I'm not 100% sure if I made the right move or not, can anyone help?
Thanks in advance.