Hi Guys.
What exactly is the 13Amp plug fuse protecting? Appliance or cable? I often come across 13 Amp fuses that are clearly original supply but should IMHO be 5 0r 3 Amp. Typically this occurs on Fridges and Vacuum Cleaners.So I change it acording to the running current (and considering starting current) but I wonder if the manufacturer knows something that I don't?
Cheers
Pete
 
Hi Guys.
What exactly is the 13Amp plug fuse protecting? Appliance or cable? I often come across 13 Amp fuses that are clearly original supply but should IMHO be 5 0r 3 Amp. Typically this occurs on Fridges and Vacuum Cleaners.So I change it acording to the running current (and considering starting current) but I wonder if the manufacturer knows something that I don't?
Cheers
Pete

the appliance the cable should already be rated to the appliance
 
The fuse in a plug is there to primarily protect the flex, but generally will protect the appliance also.

With fridges and and vacuum cleaners there will be higher than normal inrush currents and hence these items tend to have a higher rated fuse than normal.
 
Fuses, like MCB's protect the cable they supply from being damaged by over current. There are no fuses in plugtops where I am and I have mixed feelings about them because it's so easy to replace it with one that's incorrectly sized plus they're unlikely to blow unless the overload is severe such as a fault current (in which case the circuit is already protected in the DB or CU) but they're very sloppy when it comes to marginal overload such as too may items plugged into an extension lead.

If the manufacturer supplied the appliance with a 13A plug fuse then you should stick with that rating unless there's an obvious reason not to.
 
Yep I have lost count following a "professional" PAT testers who never bothered to check the fuses with me changing 13A to 3A fuses
 
I regularly encounter manufacturer fitted supply cords .50/.75 fitted with 13A fuses. Piezzo igniter in hobs being an example.

3rd ed cop...

15.14 (page 82 2nd para) Quote:
The fuse in the plug is not fitted to protect the appliance...the fuse in the plug protects the flex against fault and can allow the use of a reduced csa flexible cable.


Quote:
if the appliance needs a fuse to comply with its manufacturing standard, it should be fitted in the appliance
 
The plug fuse is there to protect the appliance flex, but the good book does say, appliances up to 700w 3a fuse, 700w and upwards 13a fuse, in any event, the fuse stated by the manufacturer should be fitted where that is known.

Cheers...........Howard

PS the good book is the COP for in service insp and test of electrical equipment.
 
I regularly encounter manufacturer fitted supply cords .50/.75 fitted with 13A fuses. Piezzo igniter in hobs being an example.

3rd ed cop...

15.14 (page 82 2nd para) Quote:
The fuse in the plug is not fitted to protect the appliance...the fuse in the plug protects the flex against fault and can allow the use of a reduced csa flexible cable.


Quote:
if the appliance needs a fuse to comply with its manufacturing standard, it should be fitted in the appliance

In the case above a manufacturer flex of 0.75 should have a moulded plug fitted and should have a length under 2M and this is allowed to be fused at 13A under BS1363
 

Reply to Fuse Size in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
414
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
1K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock