Hi,
I'm to install an extracter fan with a timer in a a brand new shower room. I got a question.
I also bought a 6A 3 pole fan isolator from Crabtree, it included instructions with diagrams on how to wire up a timed fan, to my dismay the diagram did not include a fused spur as it was coming from the light, is that allowed/right?? Just from the ceiling rose, to the isolator then to the fan.

The instructions from the fan says it needs a 3A fused spur and thought I agree. I've got into a bit of a muddle on how to wire up the fan which is operated when pull cord is pulled both the light and fan comes on, when switched off the light goes off but the fan remains running for a few more mins and thinking how do I include a 3 fused spur and drew a diagram below. (it includes 3 core +E and Tin and earth cables.
Please advise if wrong or unsuitable... http://imageshack.us/photo/my-images/32/fanwiring.png/
Many ThanksFan Wiring.jpg
 
Last edited by a moderator:
that's really the only way, as you need bothe the L feeds, permanent and switched to the fan to be on a 3A FCU, so put the FCU before the light. 1 question, though. is the circuit RCD protected? it needs to be.
 
Yes it is RCD protected also added a new )RCD protected 5 way CU near the existing CU. The isolator, pull switch and fsu will be outside the shower room.
 
Are you sure thats only a 3 pole switch ??
There are 6A 4 pole switches on the market for isolating fans. I'm based in Ireland, but we use them all the time. Dont normally include a FSU, as they are only fused in one pole. Your wiring diagram is fine, but remember your only fusing the perm live, the switch live is unfused..
 
Are you sure thats only a 3 pole switch ??
There are 6A 4 pole switches on the market for isolating fans. I'm based in Ireland, but we use them all the time. Dont normally include a FSU, as they are only fused in one pole. Your wiring diagram is fine, but remember your only fusing the perm live, the switch live is unfused..

What do you isolate with the fourth pole? Earth? All a fan requires is L, SL, N and E so can't think what else you could switch. :confused:
 

Reply to Fused spur fan in the Australia area at ElectriciansForums.net

Similar Threads

Wiring cooker hood into a switched fuse spur with a 13amp fuse in the spur. The cooker hood is 3amp. Should I swap out the 13amp fuse in the spur...
Replies
2
Views
301
Looking for counsel / guidance to replace an original Dayton On/off with speed control switch. I’ve checked with a couple local electrical supply...
Replies
5
Views
611
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Hello, I currently have two switches in my bathroom. One controls the lights above the sink and the other controls a light above the toilet and...
Replies
0
Views
733
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
638

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock