  1. Wilson12
    Offline

    Wilson12 Trainee Trainee Access

    Location:
    London
    hello I've seen the page at the back of the regs book but nothing explains can you -
    Have a spured socket off the ring using one cable and then put a fused spur after the spur and then feed additional sockets after the spir
     
  2. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    And the question is?
     
    • Like Like x 1
  3. Pete999
    Online

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Business Name:
    None
    I take it Wilson that you are referring to Appendix 14 of BS7671, the diagram shows all scenarios for a RFC and indeed the requirements for installing spurs from the RFC.
    Your question would be a no you can't spur a socket using a single cable, and then add a fused spur to supply more sockets. What you could do however is swap the Spurred socket for a fused spur and then add as many sockets as you like, what you are suggesting amounts to 2 spurs from the same point. Hope this helps.
     
    • Agree Agree x 3
  4. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Can you draw what you are asking. But it sounds like no, if I understand you correctly. Although saying that it hasn't stopped many others from doing so from what I see when attending various sites.
    Aha manitas de plata has beat me to it.
     
  5. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    There is nothing to stop you having two spurs from the socket on the ring.
    One spur to the additional socket, one spur to the FCU/

    There is a physical problem of cramming 4 x 2.5 conductors into the back of the socket.

    If I was you, I would do as Pete says above
     
  6. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    If I read correctly then no you can't do what you suggest. Think about the maximum potential load on the first section of cable spurred from the ring.
     
  7. Pete999
    Online

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Business Name:
    None
    TTC I think the OP was wanting to spur off of a socket to another socket using a single 2.5, and then from that spurred socket to another fused spur to feed some more sockets
     
  8. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    Ahh ok. Spur to FCU then on to additional sockets.
     
  9. Pete999
    Online

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Business Name:
    None
    Original socket to new spurred socket to FCU to feed more sockets. I'm getting a headache now. What you said above is how it should be done, now where are the headache pills?
     
  10. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    Like this I believe.


    2017-10-12 11.46.37.jpg
     
    • Like Like x 2
    • Funny Funny x 2
  11. Pete999
    Online

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Business Name:
    None
    Correcta munda, mon ami, zat is what I believe Monsewer OP meant.
     
  12. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    Which he cannot do. as the FCU would be a spur from a spur.

    The FCU must be before the first double socket.
     
    • Agree Agree x 1
  13. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    FullSizeRender 2.jpg COMME CA
     
  14. MisterE
    Offline

    MisterE Regular EF Member

    Location:
    Stoke-on-Trent
    and you are never 39 and a quarter :D
     
  15. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    You're right. I'm not quite up to the quarter. More like 39 1/8
     
  16. Risteard
    Offline

    Risteard Electrician's Arms

    Location:
    Derry, Ireland
    Business Name:
    Walsh Electrical Services
    Many would not agree that this is acceptable, as you are not supposed to concentrate loads at one point on the ring. Indeed, the informative appendix mentioned does not allow such an arrangement. However, as the appendix is informative it does not actually form part of the Wiring Regulations.
     
  17. Pete999
    Online

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Business Name:
    None
    Whilst I agree with Risteard that Appendix 14 is an informative Appendix, saying that it doesn't form part of BS 7671 "The Regulations" When you actually read APP14 it does quote several Regulation Number414.4
    and there are references to several chapters, and I quote 433.1.204 which need to be referenced in conjunction with Appendix 14, so I'm sorry to disagree Risteard, but I find it hard to agree with your statement, no disrespect intended.
     
  18. spinlondon
    Offline

    spinlondon Trusted Advisor

    Location:
    Harlow Essex
    It's informative, it's not the Regulations.
    Yes it may be in a book called 'Requirements for Electrical Installation', but that doesn't mean anything.
    All it does, is inform you certain methods for complying with the Regulations (well not actually the Regulations, cos these are requirements, not Regulations).
    So just to clarify, although appendix 15 is in the book we call the 'Regulations', it's not actually in the 'Regulations'.
    It's part of the book which we call the 'Regulations', but it's not part of the 'Regulations'.
    Hope that clears everything up.
     
  19. Andy78
    Offline

    Andy78 Trusted Advisor

    Location:
    Kingston upon Hull
    The book called "IET wiring regulations" ? ;)
     
    • Agree Agree x 1
  20. spinlondon
    Offline

    spinlondon Trusted Advisor

    Location:
    Harlow Essex
    Depends whether you look at the front, or on the spine.
    Anyway, that's beside the point.
    Just because something is in a book called the 'Wiring Regulations,' doesn't mean it's part of the Regulations.
    Ok?
     
    Last edited: Oct 13, 2017
  21. Pete999
    Online

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Business Name:
    None
    So with than analogy, just because "GENISIS is in the Bible doesn't make it part of the Bible?
     
  22. spinlondon
    Offline

    spinlondon Trusted Advisor

    Location:
    Harlow Essex
    Yes, exactly.
    Just because it's in the Regulations, doesn't mean it's in the Regulations.
    Hope that clears that up.
     
  23. Pete999
    Online

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Business Name:
    None
    Confused.com
     
    • Like Like x 1
  24. telectrix
    Online

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    simple pete. just because Genesis play at the Liverpool Docks, it don't mean that they're dockers.
     
    • Funny Funny x 1
Loading...
Similar Threads - Fused spur ring Forum Date
Adding fused spur for bathroom extactor Electrical Forum Yesterday at 4:12 PM
Fused Spur Combined Socket Electrical Forum Oct 31, 2017

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job