Discuss fuses/protective devices in the UK Electrical Forum area at ElectriciansForums.net

can anyone explain per-arcing i2t, arcing i2t, total let through energy. in relation to fuses/protective devices

Pre-arcing I[SUP]2[/SUP]t is the energy required to take the fuse element to the point where it starts to melt.
Arcing I[SUP]2[/SUP]t is the energy required to melt the fuse element.
Total operating, let through I[SUP]2[/SUP]t is the total energy until the arc is quenched.
The arc is caused by the fuse element melting and breaking the fault current.

Although protective devices may easily discriminate with each other under overload conditions, they may not under fault conditions, so a check is necessary to determine discrimination under fault conditions.
In order to achieve fault discrimination between two fuses:- the total operating, let through I[SUP]2[/SUP]t of the lower nominal rated device should be less than the minimum pre-arcing I[SUP]2[/SUP]t of the higher nominal rated device.

Since the relevant British Standards allow a certain manufacturing tolerance within which the design of the fuse characteristic can be made by the fuse manufacturer, therefore it is important to refer to specific manufacturers data when determining discrimination under fault conditions. It is considered prudent to allow a margin of safety between the two values to avoid nuisance blowing which may occur between fuses of different manufacturers.
As a rough guide (Rule of Thumb), fault discrimination will usually be achieved if the higher nominal rated fuse is twice the nominal rated value of the smaller fuse.
 
Last edited by a moderator:
In order to achieve fault discrimination between two fuses:- the total operating, let through I[SUP]2[/SUP]t of the lower nominal rated device should be less than the minimum pre-arcing I[SUP]2[/SUP]t of the higher nominal rated device.

You're quite right, and this is something which many sparks either know nothing about or just don't pay attention to!
 

Reply to fuses/protective devices in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

With AFDD's still being a widely discussed topic, we have put together a guide that either you or your apprentices may find useful! Electrical2Go...
Replies
0
Views
1K
I am using a 160watt-200watt multi uv tube stand alone sunbed,When the 2 power leads (plugs protected by 2x13amp fuses) plugged into a double wall...
Replies
9
Views
724
These are going to become the norm aren't they? I've been reading this...
Replies
10
Views
1K
Hi there I have a few questions related to the power ratings of certain devices and how this interplays with the fuse. The reason I am asking...
Replies
4
Views
959
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock