Discuss Fusing of fans to comply with manufacturers recommended instructions in the Electrical Forum area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. garaoke
    Offline

    garaoke EF Member

    Location:
    irvine
    Manufacturers want there fans fused to 3a on the permanent feed but the switch wire is still on the 6a MCB doing an eicr is a c2 if there is no RCD protection
     
  2. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    I assume you mean as it in a bathroom or because the cable is buried in the wall? C3 for both if to a previous edition of the regs ie full supplementary bonding was in place if not C2.
     
  3. mattg4321
    Offline

    mattg4321 Electrician's Arms

    Location:
    South East
    If manufacturers want a 3a fuse, why don't they bloody well fit one inside the fan. Bloody irritating this!
     
    • Agree Agree x 12
    • Like Like x 2
    • Winner Winner x 1
  4. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    A lot of lighting manufacturers do exactly that.
     
    • Agree Agree x 1
  5. wirepuller
    Offline

    wirepuller Forum Mentor

    Location:
    south uk
    IMO if there is a 3a fuse on the permanent line then it complies with manufacturers instruction. The switched live is only a trigger, the fan uses the permanent line to operate so a fuse on that line will serve the purpose intended.
     
    • Agree Agree x 1
  6. garaoke
    Offline

    garaoke EF Member

    Location:
    irvine
     
  7. garaoke
    Offline

    garaoke EF Member

    Location:
    irvine
    Switch left on is a supply to the timer at a higher rating than the feed
     
  8. wirepuller
    Offline

    wirepuller Forum Mentor

    Location:
    south uk
    The motor runs on the permanent line though, it wont run at all just on the switch line.
     
    • Like Like x 1
  9. garaoke
    Offline

    garaoke EF Member

    Location:
    irvine
    If manufacturers want 3a protection they should provide it
     
  10. leebut
    Offline

    leebut Regular EF Member

    Location:
    Bury
    Why not just wire the bathroom with a 3 amp fuse to the lighting and fan then wire everything downstream off the fused spur, problem solved
     
    • Like Like x 2
  11. Richard Burns
    Offline

    Richard Burns Respected Member

    Location:
    Cambridgeshire
    Business Name:
    Richard Burns
    The manufacturers want both permanent and switch line fused by a single fuse and since this involves the wiring outside the fan they cannot install a fuse in the fan.
    If they only wanted the permanent line fused they could do this, but do not because that is not their intention.
    From a fusing point of view the fuse is there to prevent cables being overloaded and causing fire.
    From a protective point of view the fuse should disconnect the power to a piece of equipment.
    Fusing the permanent line only will do the former but not the latter.
    Someone removing the fuse or finding the fuse had blown might work on the fan not realising there was still a live supply to the fan (if the switch was on), though they should check for dead at the equipment and not just at the supply.
    For coding this is down to the inspector, the lack of RCD protection would be a situation where in case of a fault it could give rise to danger, the lack of a 3A fuse on the switched line would be a far lower risk and almost minimal if a 3P isolator were fitted, so the coding would apply to the lack of RCD protection.
     
    • Like Like x 3
  12. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    I’m sure this has been said before but
    I’ll do it again…

    A 3amp fuse on a (usually lighting) circuit that is protected by a 6amp MCB is pointless. The MCB will trip a long time before a 3A fuse will pop.

    I’ve a feeling the 3A thing originally came from when the fan may be powered from something like a ring final which has a much higher current rating.
     
    • Like Like x 4
  13. leebut
    Offline

    leebut Regular EF Member

    Location:
    Bury
    A lot of electricians forget that the wiring regulations stipulate that a manufacturers instructions supersedes the wiring regulations, so if a manufacturer states they require a 3 amp fuse on that product you have to install a fuse on the circuit like I mentioned previously the best way to cover this point is to install a 3amp fused spur at the loop then everything from that point onwards is protected by that fuse on both permanent and switched conductors, the idea of the 3amp fuse is to cover every eventuality on an installation from a BS 3036 fuse through to BS60898 MCB or BS61009 RCBO, I agree the MCB/RCBO would trip quicker than the fuse but at least the installation would comply with the manufacturers instructions.
     
    • Agree Agree x 1
    • Disagree Disagree x 1
  14. wirepuller
    Offline

    wirepuller Forum Mentor

    Location:
    south uk
    Some time back there was an instance of one of these fans causing a fire, presumably it seized. It ended up in court and the manufacturers gettout was that a 3a fuse had not been fitted as per instructions. This despite the fact that we all know a 3a fuse would make no difference.
     
    • Informative Informative x 1
  15. leebut
    Offline

    leebut Regular EF Member

    Location:
    Bury
    Completely agree I remember reading the same article in one of the trade magazines, the blame was put back onto the installer
     