So why would a board change be notifiable? Essentially all you are doing is changing the OCPD a handful of times.
Not sure of the reasons, but in the case discussed only one circuit is being altered, looking at the "Wiring Matters article" changing a CU does not constitute any Minor Works, their words not mine,
 
You do not have to change from radial to ring.
You do not have to change the MCB from 16A to 32A.
What you do have to do, is provide RCD protection for the new sockets.
This can be by using RCD sockets, swapping the 16A MCB for an RCBO, installing an RCD before the garage CU or by providing RCD protection at the house.
Dare I ask what the OCPD is for the garage submain?

Dare I ask what the OCPD is for the garage submain?
I will check this out since I'm not sure whether it is from an OCPD in the house CU.
 
You do not have to change from radial to ring.
You do not have to change the MCB from 16A to 32A.
What you do have to do, is provide RCD protection for the new sockets.
This can be by using RCD sockets, swapping the 16A MCB for an RCBO, installing an RCD before the garage CU or by providing RCD protection at the house.

Thank you for all the above, it's much appreciated.
I'm going to extend the radial with four additional D/Skts.
After ascertaining whether the garage supply from the house is from an OCPD or the garage CU has its own inbuilt, I'll exchange the 16A mcb for a 16A RCBO.
The garage CU shows RCCB protected 63A 30mA. I will check this out but read this as being adequately protected?
 
Thank you for all the above, it's much appreciated.
I'm going to extend the radial with four additional D/Skts.
After ascertaining whether the garage supply from the house is from an OCPD or the garage CU has its own inbuilt, I'll exchange the 16A mcb for a 16A RCBO.
The garage CU shows RCCB protected 63A 30mA. I will check this out but read this as being adequately protected?
Dare I ask what size cable you will be using, and what method of installation, if the house CU has RCD protection and the Garage feed is coming from a cb on the RCD side of th CU (assuming it's not an amd 3CU) then all you need do is change the cb in the CU for a 20A, you don't want to go sticking RCDs Willy Nilly all over the shop, If as you mention the garage CU has an RCD then you will be covered. More than 1 RCD in the same circuit will only cause tripping problems.
 
In fairness to hightower there is certainly a train of thought that altering the protective device makes it no longer minor works (or suitable for a MEIWC) and that you are essentially creating a new circuit (although all/most of it has already been wired).
 
Old? The coals are permanently warm!
NICEIC never off the burner, simmering in the background.
In fairness to hightower there is certainly a train of thought that altering the protective device makes it no longer minor works (or suitable for a MEIWC) and that you are essentially creating a new circuit (although all/most of it has already been wired).
It's a difficult one this, although whilst I understand HT's thinking, it's still just an alteration, you could say you are creating a new circuit if you add, say 3 more twin sockets to a radial with just 1 original socket, I going to stick with MNWC, as an altered circuit, sorry HT.
 
I wish you lot would get all emotional when I talk out my ****, as I often do :)

I seem to recall I made a similar blunder last year, on this very subject. Which resulted in outright commendation & derision (you took the mick). But least I had the strong moral character (get used to looking a ----), and post the reply back from my scheme (document #15) o_O
 
I wish you lot would get all emotional when I talk out my ****, as I often do :)

I seem to recall I made a similar blunder last year, on this very subject. Which resulted in outright commendation & derision (you took the mick). But least I had the strong moral character (get used to looking a ****), and post the reply back from my scheme (document #15) o_O
When do you ever talk out of your backside?
 
Quite often I wake up in the morning Pete, particularly at weekends, and can't remember making the remarks in a post from the night before. :eek:

I reckon someone's hacked my account and making spurious remarks. I think that's 'wear' or all those bad grammars things come from, that sparksburntout picks me up on.
 
Last edited:
Quite often I wake up in the morning Pete, particularly at weekends, and can't remember making the remarks in a post from the night before. :eek:

I reckon someone's hacked my account and making spurious remarks. I think that's 'wear' or those bad grammars things come from, that sparksburntout picks me up on.
You're lucky, I sometimes can't remember what I said 5 minutes ago, who are you and what do you want?
 
xcuse my ignerrrence, but wat is a forum?
 

Reply to Garage Sockets Regulations in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
407
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
997
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
598
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
741

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock