Discuss Garage Sub Board SWA sizing in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
116
Evening folks. Quick question, I am installing a garage sub board which will have TT earthing. It has a 40A 30mA RCD main switch and I will be putting a B16 and B6 in the board. Would you size the SWA for the breakers i.e. 22A or for the main switch 40A in case someone swaps out an MCB in the future?
 
Size it for your intended final load taking into account any correction factors cc,cs,ca,cd etc.
Or if you want to future proof it then stick an unnecessary large sized cable in at a unnecessary cost of course.
 
Cheers @davesparks that was most unhelpful. @Ian1981 I'm not sure it is unnecessary cost, bear in mind there is a 25M trench dig for the cable run. I'll give the client the option. I'm sure they'd rather pay a bit more now than 2 years time decide they want another circuit, EV charge point, 16A outlet for welding or the like and need the garden dug up again. We are not talking huge figures here lets put it into perspective.
 
Since you mentioned car charging port, that is something you definitely want to think about now rather than later as that will have a drastic difference on the swa cable size.
 
I am somewhat perplexed that someone who has a profile which indicates to being an electrician has posed such a rudimentary question, hence DSs response and the possible lack of others.
 
Gents, with respect I think you are missing the point of my question. I am not asking for help calculating the cable size etc etc. Forget any of the figures I have written in my question they are irrelevant.

Lets re-word:

I have been asked to install a sub-board which has a capacity of 40A but the design current is 22A. The feed to the board is trench dug so any future upgrade would be expensive. Would you suggest sizing the cable now to the capacity of the board in case of future upgrade or size it for the design current?
 
Gents, with respect I think you are missing the point of my question. I am not asking for help calculating the cable size etc etc. Forget any of the figures I have written in my question they are irrelevant.

Lets re-word:

I have been asked to install a sub-board which has a capacity of 40A but the design current is 22A. The feed to the board is trench dug so any future upgrade would be expensive. Would you suggest sizing the cable now to the capacity of the board in case of future upgrade or size it for the design current?
Gents, with respect I think you are missing the point of my question. I am not asking for help calculating the cable size etc etc. Forget any of the figures I have written in my question they are irrelevant.

Lets re-word:

I have been asked to install a sub-board which has a capacity of 40A but the design current is 22A. The feed to the board is trench dug so any future upgrade would be expensive. Would you suggest sizing the cable now to the capacity of the board in case of future upgrade or size it for the design current?
Give him the option? Can't go wrong
 
1.5mm 25a ,2.5 mm 33a, 4mm 43a you could use any of these for current carrying cap (not sure about volt drop etc ) and could use 25a 32a or 40a MCB at your main board but your right for the cost difference of about 20quid why not put a 4mm in
 
Gents, with respect I think you are missing the point of my question. I am not asking for help calculating the cable size etc etc. Forget any of the figures I have written in my question they are irrelevant.

Lets re-word:

I have been asked to install a sub-board which has a capacity of 40A but the design current is 22A. The feed to the board is trench dug so any future upgrade would be expensive. Would you suggest sizing the cable now to the capacity of the board in case of future upgrade or size it for the design current?

Ask the person who specified the 40A board?

I'm still at a bit of a loss as to the point of this thread, you're not making much sense from an electrical design point of view.

Who specified the 40A capacity and why? How did you establish the design current?
 
1.5mm 25a ,2.5 mm 33a, 4mm 43a you could use any of these for current carrying cap (not sure about volt drop etc ) and could use 25a 32a or 40a MCB at your main board but your right for the cost difference of about 20quid why not put a 4mm in
Where did you get those ratings from.
 
Thanks to those that managed a civilised opinion.

@davesparks / @westward10 it was a question of bare minimum or future proofing, no design required or critic on whether or not I am capable of calculating the CCC of a cable or what title I give myself in my forum profile. I have a degree in electrical engineering so I am more than capable of carrying out the the design calcs to run a cable from a house to a garage...
 
I'm all about the future proofing, i see it all the time, just a light and a socket, next thing there's a 6ft chest freezer and she's got her washing machine and tumble dryer out there too, and a heater in the winter for the dog :p
 

Reply to Garage Sub Board SWA sizing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
470
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
877
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Hi. I'm being tasked with installing an electric shower into a property that was built back in the 1980's. The main consumer unit has only 4 ways...
Replies
2
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
413

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock