Discuss gas boiler volt free contact in the Central Heating Systems area at ElectriciansForums.net

lj.l

-
Reaction score
3
Hi
I have to connect up a gas boiler and know how how to do it with a volt free room stat.
What I need to know is can I use the relay/switch on a motorised valve to control the boiler via the volt free contacts in the boiler,and use 220v room stats to control the valve.
Its a two zone system and I cant work out how to control 2 zones valves from a volt free room stat.
hope this makes sense.boiler is a volkera
Thanks in advance.
 
Yes you can use 230V stat to open valve and which in turn would close the valves switch giving you a volt free signal to the boiler. All sounds good mate.
 
if there's a lot of stats etc

i usually use 230v on the contacts and switch a relay

take the volt-free from that


less risky and eliminates induced voltage
 
Cheers ,I was a bit worried about induced voltage,there are 2 stats.I have done the job now anyway but Im back during the week so I might try that then.
 

Reply to gas boiler volt free contact in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
430
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
888
For the past few years, I have used a hydronic system (outdoor wood boiler) with both high and low temp working simultaneously. The low temp...
Replies
6
Views
750
Hi. We are looking at installing a Wiser smart heating system inc. trvs We are currently electric only, with normal rads and a Heatrae sadia...
Replies
8
Views
2K
Having wired in parallel with my cordless programmable room stat an Alexa compatible wifi switch which has failed. I want to have a app...
Replies
1
Views
600

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock