Reaction score
685
Old block of four flats now having gas installed for the first time, all gas meters together just outside front door, main earthing terminal (and earth rosd) just inside front door.
Gas pipes run to boiler in kitchen of each flat, less then 1 meter of pipework inside the flat, rest on the outside wall.
I thought the best way to bond them was to link them together (unbroken 10mm) and connect to the main earthing point inside the front door.
Now a smart alec is (correctly I have to admit) saying that the regs say bond just as pipe enters each property.
This point is boxed in, and the other end of the property from the flats MET, seems pointless and disruptive to have to bond again for each flat.
Is there some other wriggle room I can use in the regs to avoid the second gas bond for each flat (such as the gas pipe not being accessable to touch in the property or something).
 
I haven't checked for myself, but I believe in the 18th if the gas supply has an insulating sleeve meaning the supply pipe is not electrically continuous then it doesn't need bonding.
 
Thinking about it the water bond is under the boiler, can just splice into that as well so bond at the meter and bond just in the flat as well, bit of hassle but will do it where practiable.
 

Reply to Gas bonding in block of flats in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We had our gas disconnected last week and the meter removed. We need to start removing the redundant gas pipes in inside the property. There is...
Replies
6
Views
2K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K
Hi guys, has anyone got any experience of resistances through press fit plumbing fittings? Just been to a job I did last year which was a...
Replies
8
Views
1K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
Does a copper gas pipe, coming into the house require bonding when the pipe is being supplied by propane cylinders, via rubber hose. Doesn’t go...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock