Evening all,

Got a 5.75kva Generator on site powering a show home via a 32A commando plug.
I have 110 L-E 110 N-E and 222v L-N.
I have an Earth electrode in the ground feeding the E point on the gernator with a 10mm bond from the consumer unit to the same E point.

The problem i have is i cannot get a Earth path for my RCBO’s installed to test them to check the house is safe whilst on the generator.

I have a feeling i need to put a N-E link within the generator (1 side of the Tap to the earth point) before its inbuilt RCD.

Does any one have experience in this to one if it’s safe for me to do?

I have already spoken to the manufacturer but they were unhelpful and told me it should work straight out the box.

I’m just concerned if my test kit cannot see an Earth and N-E has voltage it’s unsafe as we know, no earth means the RCBO’s won’t work.
N-E is also live no matter what atm as i only have single pole McB leaving it with a potential even when the McB is open.

Hope you can help.
 
I would check that the centre point of the winding is not earthed first. It could be that the 110V either side of earth is just chance due to equal leakage from both lives, but it could be an internal connection in the generator that would be correct for a USA / Far East version. In that case, earthing one end would cause a short-circuit across half the winding, and the centre-tap-to-earth link would have to be removed first.
 
Yes i discovered that today and i put the N-E link in and it started to smoke from the alternator so i switched it off.
I agree it’s center tapped.

A way round this could i leave the Earth out of the Plug from the generator and Install an Earth steak for the house Earth.

would this be a safe way to do it if it works, or would that create a potential on the chassis of the generator in a fault condition? If so this should be covered by the generators RCD?

Is there any books i could buy to educate myself for future, so i am ready if i do a generator again?

Thanks for your reply
 
would this be a safe way to do it if it works?
No! That will make the generator chassis live at 110V to earth all the time, even when there's no other fault. The only way to make this unit usable in a TN system is to remove the CT-E link.
 
Ok where do i find that on a generator as the board shows no links, unless i take all the parts of the generator off ?
Even if the generator is steak to Earth, i would of thought it would elemiate that issue?
i was trying to create a TT for the house until power is on site, like how you would if you submain a cable to a garage and not connect the armourings at the garage end. Thought this would be the same method if that makes sense?

RCBO are standard house ones so 230v
 
To remove the centre tap, you would have to dismantle the alternator.
I believe your 230V RCBOs will not work with the generator as it is at present.
Check the generator RCD, I suspect it is rated for 110V.
 

Reply to Generator Earthing/Voltage etc in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
518
Hi Sorry to bring this one up again but have read numerous posts and answers and not got an answer specific to my situation. I have a Loncin...
Replies
8
Views
2K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...
Replies
5
Views
731
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock