Max1882

Hi all. my problem is, i had to wire a generator up to a mobile phone last. In a nut shell i have checked all 3 phases against earth and nuetral while they are in a connector block and i get 415 on all 3 phases, however when i hard wire it into the isolator and turn the changeover switch from mains to generator the voltage drops on 2 of the phases (i get 230v,200v,180v) some thing obviously is wrong in the data/control cabinet? And if there is somehting wrong why does it not affect it when there is mains power on it? The voltage dropping only happens when the mast is powered by the generator? Im going back out to the job at 6am so any help appreciated!lol. Thanks in advance....
 
i have checked all 3 phases against earth and nuetral while they are in a connector block and i get 415 on all 3 phases,
If you're getting 415v between phase and earth or phase and neutral this is a massive overvoltage. Why did you connect it up to the equipment and perform live tests in that case??


......when i hard wire it into the isolator and turn the changeover switch from mains to generator the voltage drops on 2 of the phases (i get 230v,200v,180v)
Are you testing to earth or to neutral to get those phase voltages?
 
Last edited:
Is the generator correctly rated for the load?
 
When it was wired into the isolator i checked it against nuetral and earth and it drops on both. There is even a voltmeter switch on the generator what allows me to check the voltage. I dont know the rating of the generator but they are deployed to masts all over the country so i presume it will be big enough, The physical size of it sits on a trailer so its not a small thing id expect it to be big enought to power x2 control/comms cabinets.
 
Has the Generator side of the changeover switch got fuses in?
180v is that magical figure you get back from a 3 phase load when 1 phase is missing.
 
when all 5 wires were in onnector blocks i tested all 3 phases to earth and nuetral
You should not have seen 415v between phases and neutral. 240 or maybe 250 volts maximum would be the expected voltage L1-N, L2-N and L3-N.
 
Sorry just read back, my bad..... When i was testing to earth and Nuetral i was getting 230v and across all 3 i was getting 400v. Everything was electriacally sound until i hard wire it in and turn the changeover switch to generator
 
theres no fuses, nothing trips and its hard wired into the same place on the isolator as what the mains power tails are and it works fine with mains
 
So effectively you are saying that you have full voltage supplied from the generator when under no load and when the generator is placed under load you are getting significantly reduced voltage. The generator is not being overloaded, though you could have a fault in the load that is drawing excess current.
This sounds more like a lot of loose phase connections in the generator.
 
Possibly high resistance neutral connection to the star point? Has the same effect as a duff neutral on the mains.
 
I think you have just answered your own question...."it ok on mains".....tends to suggest the generator is not beef enough.
 
Im 99% sure the generator is big enough like i say its only powering x2 control/data cabinets cant see those taking a big load. So would you say gett anoth generator deliver to site is the best bet?
 
I'd also go with the overload theory from the info given. If it was a high impedance neutral at the star point you'd probably see some phases testing high and some testing low WRT the neutral, not all 3 phase at 230v or less.
 
Have you confirmed the continuity of the neutral back to the star point?
What does the engine do when it is put under load? Does it labour or hunt or does it continue to maintain speed within reason?
What does the generators control panel have to say about it? Are there any errors reported? Does it trip/shutdown through undervoltage or underfrequency?
 
the generator continues running but you can hear a difference in the engine. Thinking about it, there is a voltmeter/ HZ meter and an ampmeter on the generator. you can turn a little knob to see the readings of all 3 phases. When the change over switch has been turned to generartor and the voltage drops the ampmeter shows 0 so its not pulling any current.
 
Hi,

Does your switch have knife blades, quite often if they are not aligned properly you can lose a phase or two. Especially if it's a new one and hasn't been used before.

Worth a check.

Regards.
 

Reply to generator fault? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
971
Good day all, I'm writing from the Commonwealth of Dominica (NOT Dominican Republic) where we have single phase 230V, 50Hz. I'm managing a...
Replies
3
Views
1K
This is quite lengthy so get comfy... I had a bizarre call out relating to a job I attended about five years ago. The situation was they were...
Replies
11
Views
1K
ATS For generator to supply warehouse when Mains Failure, a PFC Panel is in place on the Main Supply. Will this need to be Off when generator is...
Replies
0
Views
694
Hello, First of all, thank you in advance for any helpful insights posted in response to my question. I have just moved into a new home. With...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock