Guybrows

Hi

Had a phone call to go and look at moving a 44kva 3 phase generator on a farm. Im going to have to resupply it in swa. I havent done any work on a farm and i ve only ever installed temporary generators when the electricity board have decided not to turn up a day before a shop opens. I am thinking i should bury the cable 0.6m as per regs. Does anyone know if it has to be bureied. The guy on the phone was talking about taking it over a building but i want it to be done to regs. Any other advice would be greatly appreciated

Thanks guys
 
There is no reason it has to be buried other than if you do it should be deep enough that it will not be damaged hence the recomended depth of 600mm or if it is going surface it should be placed where vehicle or livestock damage will not happen, However from past experience on farms I would think carefully on the route underground as layouts change contantly with fenceposts etc.
Best advice is to keep to straight lines with solid markers (buildings etc) at direction changes, go deeper if you can and give them a layout drawing to stop damage to it later not forgetting marker tape above its route.
My guess its for a standby with auto or manual changover so earthing should also be checked but i'm sure you have that covered.
 
when you eary your genny, try to get a low reading as possible.This will entail driving 2 or more seperate rods down, at least the same distance as the deepest rod apart. Also any metalwork that can be touched at the same time as the genny frame, will need to be bonded to the genny.
 
Last edited:
when you eary your genny, try to get a low reading as possible.This will entail driving 2 or more seperate rods down, at least the same distance as the deepest rod apart. Also any metalwork that can be touched at the same time as the genny frame, will need to be bonded to the genny.

Far better to have one rod position and coupling the rods to give you the depth, rather than having 2 X 1 metre rods in 2 positions. Even better, to have the 2 rod positions each with 2 rods coupled together!!

What is important is to make absolutely sure your neutral point on the Genny is earthed via your rods, and not just bonded to the Genny frame.
 
Far better to have one rod position and coupling the rods to give you the depth, rather than having 2 X 1 metre rods in 2 positions. Even better, to have the 2 rod positions each with 2 rods coupled together!!

What is important is to make absolutely sure your neutral point on the Genny is earthed via your rods, and not just bonded to the Genny frame.


When I said rods, I meant that a number of rods screwed together still constitutes one complete rod. I wouldn't advise only sinking one length.
 
When I said rods, I meant that a number of rods screwed together still constitutes one complete rod. I wouldn't advise only sinking one length.

What i tend to do when supplying a TT earth for permanent and semi-permanent Genny's of a smaller size, is to position my earth rods diagonally approx a metre or so away from the the Genny mounting pad and run a 16/25mm bare copper conductor around the pad at around 50 to 60cm depth, linking the 2 rod positions.


Also, if the pad is substantual, with decent reinforcment, i'll also make arrangements to have to a section of rebar brought out of the pad and connect that to the earth ring. Or connect a short length of insulated earth conductor to the rebar prior to the concrete pour.

For larger stand-by, and prime power Genny's (750 KVA and above) the earth arrangement will be obviously be a good deal more involved but still based loosely on the above arrangement...

As i've stated before, i'm far more used to working with 3m 3/4'' earth rods, but nothing stopping anyone in the UK from coupling together 2 or 3, 5/8'' rods to get the depth, stability and decent Ra value
 
Had a look today and looks easy enough to run the cable using gurder clips to run the cable up and across along the steel frame of the milking parlor.

Going to do my cable calculations to get correct cable size.
The Generator(44kva) will be sitting on a concrete pad that has already been built and will be fixed down.
Where the generator is currently situated it has a bond from the frame to the steel structure of the building.

Am i correct in assuming that,

1. I will need to bond the frame of the generator to the steel frame as you can touch both at the same time

2. An earth spike shall be installed and connected to external earth connection on the frame of the generator and then check continuity between earth point and neutral connection at the generator.

3. Does the above then give me a pme at the cu that the generator is feeding thus i have no need for an earth spike at cu or the running of a separate earth from generator to cu, i'm guessing i should then do a ze at cu and get less than 20 ohms.

4. The cu has two supplies connected. the permanent generator that is getting moved being one and they also have a smaller generator that they use as a back up if the permanent generator goes down. Theoretically this allows for both generators to be supplying cu simultaneously. Is this allowed?

5. Does the installation need rcd protection or does it now become a pme/tncs system?

Thanks for all your help guys, really enjoying this one as its all new to me!
 
Can we get some piccys , when your not busy during the install


I would say that unless the two gennys can be synchronised then it would not be allowed , could be wrong ,
JAmie
 
Last edited by a moderator:

Reply to Generator on Farm in the Canada area at ElectriciansForums.net

Similar Threads

Iv been asked to wire a separator (portable to go to different farms and separate water from slurry) to a 3phase 40 kva generator. The separator...
Replies
4
Views
1K
This is quite lengthy so get comfy... I had a bizarre call out relating to a job I attended about five years ago. The situation was they were...
Replies
11
Views
1K
Just thoughts Id share my recent fun and games on my parents farm.. The electrics are old. Its a 400yr old house with outbuildings just as old...
Replies
9
Views
1K
Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
341
HI folks,, Im registered as a DIY guy..I dont do much electrical around my building except the occasional replacement of receptacles, switches...
Replies
0
Views
646

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock