Discuss getting the cut out fuse changed?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

E

essexboy

a customer needs a cu replacement and the meter tails are 16mm and the earth 10mm run from a receesed box outside the flats front door and the cut out fuse is marked up 100A.now...to upgade the meter tails nd earth is going to be a right pain in the A*** ..is it unherd to ask the dno to put a 80 amp cut out fuse to replace the 100a to save the hassle of upgrading the tails???
 
Have you had a look at the fuse itself or are you Reading the lable on the fuse carrier ,you may find it is already a 80a fuse or even a 60a which I would put money on as it's a flat.
 
Last edited by a moderator:
my thoughts exactly pennywise ,the fuse carrier is marked up at 100A and i have`nt peaked inside yet and i forgot to mention that its a 3 phase service head with Tn-cs earthing if it makes a differance?
 

Reply to getting the cut out fuse changed?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
773
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Got an EV (Nissan Townstar EV) in my house, has a Zappi EV charger installed (by myself) and notified via ENA form to Scottish Power energy...
Replies
4
Views
1K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock