    What are peoples opinions on...

    Coming from a metal wylex 80A sw/fuse in a 25mm SWA to feed a plastic consumer unit? A slight differnce of opinion on site this morning!! I'm thinking the consumer unit should be metal cased, although another spark doesn't see why, other than the strength of the board to support the gland. The armour will be earthed at the switch fuse end, and its a 3 core armour for Live, Neutral and earth.

    Am i being over cautious? Or are we both talking absolute mince?!?!
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    or a metal adaptable box under the CU. gland into that and leave tails long enough to go through into CU.
     
    • Like Like x 2
  3. Plonker 3
    Online

    Plonker 3 Guest

    Nothing wrong with doing that, as long as you remember to earth the armourings at, at least one end. As long as it is cleated correctly there shouldn't be a problem with the strength of the gland into the DB.
     
  4. mogga
    Offline

    mogga Just me Electrician's Arms

    earthing nuts are great for this BUT finding an area on the C.U. capable of taking a gland is the problem id forsee as tixyLix says galv box n tails to C.u
     
  5. Welchyboy
    Online

    Welchyboy Guest

    if you dont wanna/cant fit a galv adaptable box between cable and CU i would just bolt the banjo to the cu like normal and use an earth tail (belt n braces?), as long as the cable is supported properly thats fine
     
  6. Amp David
    Offline

    Amp David Trusted Advisor

    Location:
    Glossop
    With it being 25mm, i'd gland it into a metal box first as don't think you have much plastic left around the gland once it had been cut for the gland to enter.

    Have in the past glanded 10mm and less into plastic enclosures, but just made sure any strain was taken up by the clleats
     
  7. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    and make sure the hole at the top of the metal box is fitted with grommet strip or a bush and nut.
     
  8. Smudge
    Offline

    Smudge Electrician's Arms

    Location:
    Edinburgh
    i think a metal adaptable box is prob the best solution. Looks like we were both right in our own ways...shame, cause the loser had to buy todays gregs...
     
Loading...
Similar Threads - Glanding plastic Domestic Forum Date
10% Off THE WHOLE WEBSITE at FilPlastic.com with this code! Electrical Forum Sep 6, 2018
Domestic Plastic Light fitting with metal trim & no CPC DIY Electrical Forum Aug 30, 2018
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job