Hi, Got a Glow-worm 18hxi boiler (6yrs old) with an intermittent fault.
Cuts out with F1 or F4 code message. Sometimes runs for several days with no problem, then cuts out once or twice same day. Regularly serviced by our local plumber (also fitted it) but he cannot find the problem. Had the burner door seals renewed/condensate drain/gas pressure/flue checked with no problems found. Contacted a local boiler specialist who thought it could be the old style ignition electrode. He fitted a new one but it did not solve the problem.

Any suggestions would be greatly appreciated

Thanks
 
F1 code says Ignition fault, no gas, insufficient gas, gas valve adjustment, electrode ignition lead or igniter + connections defective and air inlet duct. All of these have been checked I believe.
F4 code says as F1
 
Hi, Got a Glow-worm 18hxi boiler (6yrs old) with an intermittent fault.
Cuts out with F1 or F4 code message. Sometimes runs for several days with no problem, then cuts out once or twice same day. Regularly serviced by our local plumber (also fitted it) but he cannot find the problem. Had the burner door seals renewed/condensate drain/gas pressure/flue checked with no problems found. Contacted a local boiler specialist who thought it could be the old style ignition electrode. He fitted a new one but it did not solve the problem.

Any suggestions would be greatly appreciated

Thanks


"Hello legoman",


As You have had your Boiler looked at by 2 Heating Engineers and the Fault code identified problems have been investigated and attempts have been made to rectify these to no avail I would strongly suggest that You contact Glow Worm Boilers and at least discuss these facts with their Technical department - or get your Boiler Installer to speak to them.

If as I suspect they state that in light of your Engineers attempts to address the Fault Code issues to no avail a Glow Worm Engineers visit is definitely required I would strongly advise You to arrange and pay for this as their Boiler Engineers are obviously `Experts` on Glow Worm Boilers.

And if they are actually working direct for Glow Worm they will have no desire / motive for changing and charging for multiple different parts to try and find the problem - as unfortunately some Independent `Boiler Engineers` do - I don`t mean the Engineers that You have used up to now.

However if You mention the Fault codes and what has already been tried etc. when you are booking a Glow Worm Boiler Engineers visit they might arrive with various other parts that could be associated with the sequences leading to the creation the Fault codes and they would be able to try replacing some associated components.

What You have described sounds to Me as if it could be an intermittent Gas Valve problem - OR an intermittent Electronics problem which somehow is producing `False Fault Codes` - BUT - I am NOT an expert on Glow Worm Boilers and I have not installed one for over 10 Years as I favour other manufacturers Boilers.

As the Fault are intermittent it is obviously very awkward if the Fault does NOT display at the time of their visit - BUT You should write out some Notes listing everything that You have observed about the Boiler Faults - and what your 2 Heating Engineers have done to try and fix the problems - that should help a Manufacturers Boiler Engineer with diagnosing possible causes even if they are not in evidence at that time.



I hope that You do take up my suggestion and go to Glow Worm and arrange an Engineers visit - after all the Manufacturers Boiler Engineer MUST be able to diagnose and solve the problem - how can they NOT !

They should have the attitude that they can diagnose and solve ANY Fault - even from a good description - although most Faults are confirmed by actually electrically testing components and finding them to be Faulty at the time - so if a malfunction is NOT displaying at the time it could be impossible to be sure of the cause.

Regards,


Chris
 
Last edited:
i have the same problem with my glowworm 30 cxi.
i reset it and it clears.
have you found the fault yet?
first time it happened i had to cut back and determinate the fly lead that powers the ignitor as it was very corroded and about to snap.
i use to get many faults with this boiler mostly blocked heat exchangers and broken diverter valve.
hope yours gets sorted.
 
applemac.

I have not found the fault yet. Took Chris's advice and phoned Glow-worm. Spoke to very helpful guy (Piers) but was told he will only explain possible solutions to gas engineer. I had a problem with blocked H/E few years ago (leak in C/H pipework) Had H/E cleaned OK.
Annoying thing about my problem is, I can go several days with no faults showing, and then get 3 in a day!
When the guy checking my boiler comes back to me, I am going to ring Glow-worm and ask them to offer their advice to him. Will post if this is a success.
 
applemac.

I have not found the fault yet. Took Chris's advice and phoned Glow-worm. Spoke to very helpful guy (Piers) but was told he will only explain possible solutions to gas engineer. I had a problem with blocked H/E few years ago (leak in C/H pipework) Had H/E cleaned OK.
Annoying thing about my problem is, I can go several days with no faults showing, and then get 3 in a day!
When the guy checking my boiler comes back to me, I am going to ring Glow-worm and ask them to offer their advice to him. Will post if this is a success.


That at would be great mate, I also get a rumble- slight booming noise?
 
applemac.

I have not found the fault yet. Took Chris's advice and phoned Glow-worm. Spoke to very helpful guy (Piers) but was told he will only explain possible solutions to gas engineer. I had a problem with blocked H/E few years ago (leak in C/H pipework) Had H/E cleaned OK.
Annoying thing about my problem is, I can go several days with no faults showing, and then get 3 in a day!
When the guy checking my boiler comes back to me, I am going to ring Glow-worm and ask them to offer their advice to him. Will post if this is a success.


"Hello again legoman",

I was fairly sure that the Glow Worm technical department would state `We will only give technical advice to a Gas Safe registered Gas Engineer` - but I thought that they might state from your descriptions that one of their Boiler Engineers would need to attend to your Boiler in which case You would have been the person who had to arrange that.

I hope that when your Heating / Boiler Engineer speaks to them they can advise on how to rectify the faults without too much expense regarding replacing parts.

It may still come down to arranging and paying for a Glow Worm Boiler Engineer to visit as they would be `Duty Bound` to be able to diagnose and rectify the fault / faults - and while at your Home if necessary they could talk through their findings with their Technical Department as they carry out various tests on the Boiler components - this should enable them to resolve matters.

BUT - IF no Faults were displaying on that visit because of the intermittent nature of the faults that obviously would complicate matters unless the descriptions from You and your Heating Engineer enabled the Boiler Engineer to know what had been happening to cause the problems.


Good Luck with getting your Boiler sorted out.

Regards,

Chris
 
"Hello legoman",

Did You manage to get your Boiler sorted out ?

I would be interested in what was found to be at fault ?

Regards,

Chris
 
Chris.
No I have not. My boiler specialist came a week ago and while he was there I rang Glow-worm Tech support and we tried adjusting some of the settings IE-gas pressure, %CO etc to optimal.
Before this I had run for 12 days with no faults....maybe I should have forgotten about it, because since it was "tweaked" it has tripped at least once every day!
I spoke again to Glow-worm this week and they said "there could be a problem with the igniter unit" or if not it may be the PCB. I can buy an igniter unit for £30.00 but I'm not really sure what to do. Every time my boiler specialist comes, it is costing me. I am tempted to "bite the bullet" and get a new boiler fitted...something like an Ideal Logic with a 5 year warranty.

Whatever happens I will ask my B/S what he changed on Glow-worms advice and let you know if you wish.

Also, just to be sure I had National Grid round to check the meter. The guy said there were no problems re-water in the gas and the gas pressure was fine. He fitted a new regulator as my old one was a bit tatty.
 
The days when you could fit and forget a boiler for the next 20 years are over.

Now you buy a boiler which comes with a nice five year warranty and in the sixth year it becomes Life Expired - or as we in the trade say Donald Ducked.
 
Chris.
No I have not. My boiler specialist came a week ago and while he was there I rang Glow-worm Tech support and we tried adjusting some of the settings IE-gas pressure, %CO etc to optimal.
Before this I had run for 12 days with no faults....maybe I should have forgotten about it, because since it was "tweaked" it has tripped at least once every day!
I spoke again to Glow-worm this week and they said "there could be a problem with the igniter unit" or if not it may be the PCB. I can buy an igniter unit for £30.00 but I'm not really sure what to do. Every time my boiler specialist comes, it is costing me. I am tempted to "bite the bullet" and get a new boiler fitted...something like an Ideal Logic with a 5 year warranty.

Whatever happens I will ask my B/S what he changed on Glow-worms advice and let you know if you wish.

Also, just to be sure I had National Grid round to check the meter. The guy said there were no problems re-water in the gas and the gas pressure was fine. He fitted a new regulator as my old one was a bit tatty.


"Hello legoman",

Thanks for the update - Sorry to hear that You are still having problems despite technical advice from Glow-worm.

I would still advise finding out the cost of a Glow-worm Boiler Engineers visit and possibly replacing the PCB - before having a new Boiler installed.


I am not doubting the skill and knowledge of your Boiler specialist in any way but in your position I would want to put this onto Glow-worm - as I mentioned before how can they NOT be able to rectify the fault ?

Even if they had to visit more than once because of needing a part they the Engineer did not have on the first visit how could they justify any excessively High labour charges - but please confirm the charges for more than one visit if You do speak to them.


I would speak to Glow-worm again yourself - the Servicing & Repairs / Engineers visits department.


I would tell them that You would like to have your Boiler repaired by them because You do NOT want to hire an Independent Gas Engineer / Boiler Repair Company as You have heard about them sometimes not knowing what is faulty and then changing PCB`s / multiple parts to TRY and solve the problem when the part was not faulty - a `Trial & Error` method of Boiler Repair.

You want Glow-worm to GUARANTEE that they as the Manufacturer will repair the fault on your Boiler - without changing / charging for multiple parts to `narrow down` the faulty component.

As the Manufacturers Engineers I feel that they have an obligation to repair your Boiler in a correct / cost effective manner - any `Trial & Error` changing of parts which are then found to NOT rectify the fault should be non chargeable to You [at least the parts].

I would tell them at the time of booking the Engineers visit that you have had a Boiler Engineer follow some suggestions from their technical department - but now that this has NOT solved the problem and obviously He cannot try changing various parts because You would have to pay for them - whereas a Glow-worm Engineer would possibly have the facility to try replacing parts to see if they solved the problem without charging You if they subsequently had to remove them again.

You now want their Engineer to use their specialist expertise of their Boiler / probable access to spare parts at the time of His visit to diagnose and rectify the problem.


I hope that You do manage to get your Boiler repaired - I would be very interested in the outcome if You could put an update on here.


Regards,


Chris
 
Last edited:
"Hello legoman",

Thanks for the update - Sorry to hear that You are still having problems despite technical advice from Glow-worm.

I would still advise finding out the cost of a Glow-worm Boiler Engineers visit and possibly replacing the PCB - before having a new Boiler installed.


I am not doubting the skill and knowledge of your Boiler specialist in any way but in your position I would want to put this onto Glow-worm - as I mentioned before how can they NOT be able to rectify the fault ?

Even if they had to visit more than once because of needing a part they the Engineer did not have on the first visit how could they justify any excessively High labour charges - but please confirm the charges for more than one visit if You do speak to them.


I would speak to Glow-worm again yourself - the Servicing & Repairs / Engineers visits department.


I would tell them that You would like to have your Boiler repaired by them because You do NOT want to hire an Independent Gas Engineer / Boiler Repair Company as You have heard about them sometimes not knowing what is faulty and then changing PCB`s / multiple parts to TRY and solve the problem when the part was not faulty - a `Trial & Error` method of Boiler Repair.

You want Glow-worm to GUARANTEE that they as the Manufacturer will repair the fault on your Boiler - without changing / charging for multiple parts to `narrow down` the faulty component.

As the Manufacturers Engineers I feel that they have an obligation to repair your Boiler in a correct / cost effective manner - any `Trial & Error` changing of parts which are then found to NOT rectify the fault should be non chargeable to You [at least the parts].

I would tell them at the time of booking the Engineers visit that you have had a Boiler Engineer follow some suggestions from their technical department - but now that this has NOT solved the problem and obviously He cannot try changing various parts because You would have to pay for them - whereas a Glow-worm Engineer would possibly have the facility to try replacing parts to see if they solved the problem without charging You if they subsequently had to remove them again.

You now want their Engineer to use their specialist expertise of their Boiler / probable access to spare parts at the time of His visit to diagnose and rectify the problem.


I hope that You do manage to get your Boiler repaired - I would be very interested in the outcome if You could put an update on here.


Regards,


Chris



"Hello Legoman",


I hope that You don`t think that I am pestering You - I wondered what happened about getting the fault on your Boiler rectified ?

It is always interesting to Me to find out the causes of Intermittent faults and for the OP`s to post them on here because the result may help someone else in the future.

I hope that You have managed to get it sorted out - could You let Us know what happened Please.

Regards,

Chris
 
"Hello Legoman",


I hope that You don`t think that I am pestering You - I wondered what happened about getting the fault on your Boiler rectified ?

It is always interesting to Me to find out the causes of Intermittent faults and for the OP`s to post them on here because the result may help someone else in the future.

I hope that You have managed to get it sorted out - could You let Us know what happened Please.

Regards,

Chris
Chris,

No problem.
I have not done anything as of yet.


After optimising my settings through the Glow-worm tech dept, the boiler tripped at least once a day. Something I then did (14th Mar), was to put a small piece of tape across the bottom section of my Flue. I read this on another board some time ago, and thought I'd give it a try. All my settings were adjusted to optimal before this so, not sure if it is making a difference. The weird part of all this is, since I last posted, my boiler has only tripped once.

My B/S suggested I ring him after my hols and gave me a price to change my old boiler.

The thing is, I have solar panels with a control switch to my immersion heater which I put together, that allows me to turn my boiler off from now until the end of October as far as hot water is concerned...unless we have a spell of exceptionally dull weather so, I may just leave things as they are for now.

Hope this helps
Will update if there are any changes or I swap boiler.
 

Reply to Glow-worm 18hxi intermittent fault in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Hi I don’t know how resolve this so any helpful advice would be greatly appreciated. I have no electrical knowledge. I will try to be as clear...
Replies
57
Views
11K
Hi, I've got a problem with my boiler I was hoping someone might know what it could be (apologies for me explaining in very simple terms), we've...
Replies
46
Views
10K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock