- Reaction score
- 479
For some reason, the grenfell tower inquiry has got an american electrical expert to comment on the electrical cause of the fire. And he doesn't seem to know a lot about BS7671 etc,
Firstly he thinks you can't trip an RCD after the MCB has tripped of a given circuit (presumably they have DP MCBs over there?), and secondly he thinks it's very improbable to trip an RCD and MCB simultaneously. Therefore he thinks most likely this happened in the first few minutes of the fire:
https://www.grenfelltowerinquiry.org.uk/file/2822/download?token=crUe0vAo
He also seems to think a more "violent" short circuit would be more likely to start a fire because the MCB wouldn't trip quick enough. And he uses the total clearance time (rather than pre-arc time) to decide whether there's discrimination between a B32 and a 13A fuse.
They could have got any british electrician in and they'd have done a better job than this guy!
Firstly he thinks you can't trip an RCD after the MCB has tripped of a given circuit (presumably they have DP MCBs over there?), and secondly he thinks it's very improbable to trip an RCD and MCB simultaneously. Therefore he thinks most likely this happened in the first few minutes of the fire:
https://www.grenfelltowerinquiry.org.uk/file/2822/download?token=crUe0vAo
He also seems to think a more "violent" short circuit would be more likely to start a fire because the MCB wouldn't trip quick enough. And he uses the total clearance time (rather than pre-arc time) to decide whether there's discrimination between a B32 and a 13A fuse.
They could have got any british electrician in and they'd have done a better job than this guy!