Any good storys?
You can't believe it can you, in all my years of sparkying things like this amaze me, the installer must have had the day off from tech(if he went at all) when this subject was taught. Why not just use a large male bush and locknut ? or if you must do it like the picture,put a slot between the knockouts with a jigsaw, to create in theory one hole.Here's one I spotted recently, 100a rotary isolator, 25mm tails, completed by an ELECSA AC in 2011. Nice.
View attachment 38924
I got called out to conduits getting hot after a firm moved into a new build, it turned out the electricians had run the 3phase to the switch bank for the lighting through 3 conduits and lost the cancel out effect, the conduits were that hot we couldn't hold them, the MCB's had been tripping is the original call out and when they corrected their design problem they had just replaced the metal with plastic.. the issue still effected further upstream... they didn't like a 21yr old telling them there design was to blame especially looking 5yrs younger than my real age, after lot of blame and shame from them they rectified the install to how I suggested and walked away tail tucked between their legs.
It was a poor design throughout, factory of inductive lighting run through into a 12gang grid (no contactors) if I recall, mixing phase entries up on high inductive loads was probably a key factor plus across several lighting circuits over the phases, hard to repeat on a bench I would imagine.Really? A lighting circuit causing what I'm presuming to be 20mm galv conduit to get that hot? What did they have, 50kW of lighting on each phase?
I've seen a temperature rise of a few degrees whilst playing in the workshop at low current. (low current in this case was (16 - 32A) To get anything to where I couldn't hold the metal it was >150A.
No as my rectification cured it after they tried to, it did not involve grouping factors, cable sizing etc as this still existed in other conduits downstream that were not effected, I work with motors a lot and VSD control, I have a good understanding of what can occur when you run the motors too slow through speed control and the impeller can no longer dissipate the motors normal heat generation, it can melt high temp' winding insulation off and it happens due to the runaway effect that could initially be a few degrees over its dissipation capability due to the slower impeller speed, you do not need any initial high temperature, you just need a degree or 2 more that it can remove naturally and the runaway effect can end up cooking the install.Could the high temperature of the conduit have been caused by the Ohmic heating of bundles of conductors contained inside the metal conduit whose size was inadequate for their current flow, containment, ambient temperature and demand factor? Maybe several IsquaredRs proved more troublesome than eddy current heating in this instance.