I ordered 16 x Sanyo HIT-240SE10 with a SMA 4000TL back in October last year, but due to all the FIT problems my supplier could only source HIT-235SE10 panels. No big deal and the installation went ahead on 241111. During the installation I noticed that they had installed a 3000TL so I called their sales office and they apologized for not telling me about the switch but assured me that the3000TL was a better choice for the system. I wasn’t happy, but with 12[SUP]th[/SUP]Dec looming I accepted the 3000TL and the final bill was reduced to reflect the change in equipment. I have been very happy with the installation and have been pleased to see the generation increase almost on a daily basis as the days lengthen. All was fine until today when the inverter maxed out at 3kW from12:00 to 15:00 and this is only February.

Am I looking at this happening every sunny day until November?

Is this OK or should the inverter be changed?

Regards Mike

Location:Edinburgh Facing 210[SUP]0[/SUP], Pitch 45[SUP]0[/SUP]
 
Last edited by a moderator:
The inverter is undersized, the max input for the inverter is 3200W DC. To be fair to the installer pre 12th December was a crazy time and inverters were hard to get hold of but they should give you a more suitable inverter.

You will find that often the highest output occurs in March when there is good sun and low tempretures.
 
Lots of people undersize, to much of sma software imo.
Most of your energy is produced in the bright long sunny days not in dark short days.
A company I know ..16 sharp 245w spec SB 3000 HF...16 sharp 250w spec SB 4000TL...?????
Cant work this one out myself.
 
I think people look at the Sunny Design software see the green ticks and assume that the inverter is correct and don't take any notice of the max dc input.
 
Undersizing is quite common but that seems a bit small.. would probably have been worth getting the larger one, but times were hard. Difficult to get stock. Even now its becoming a full time job sourcing inverters... Right now i'd happily swap one of the 4000TL in stock for a 3000TL i can't find....
 
bearing in mind your geographic location and orientation of your roof I would say a 4000TL is too much wheras a 3.6 inverter of some description would be ideal.
 
I agree with moggy - your current 3kW inverter is a bit too small. A 4kW is a little oversized. A 3.6kW inverter would be ideal (of which there are several; I have an Aurora 3.6).

My SouthEast-facing, 40-degree roof, 3.75kWp with 3.6kW Aurora inverter peaks out around 2.5kW at the moment, so there's still plenty more power to come as summer approaches and if you're maxed-out at the moment, you'll be losing about 25% of your potential in summer.
 
the efficiency of the 3800 is poor compared to other more modern inverters. IT's basically an older model and there are better ones out there
 
It was an emergency measure while the were waiting for the 3600TL to be released.
They were very slow filling the essential 3.6 market, it was a real gap in their range
 
Never used a lot of the Fronius Inverters- More of an Aesthetic thing :p They're bloody ugly :)

Each to their own I guess :)
I'm happy with mine, guess looks take a back seat though I don't think it's particularly ugly. It's very efficient and came with a 20yr warranty so it kind of does it for me!
 
The fronius is handy in that you can run a single string of 16panels. I've used them a lot where single string is ok as power ones were impossible to get hold of during the autumn so I only used them where I had to have 2 strings.
SMA HFs are quite nice, and no need for bonding.

Fronius aint so ugly!! kirkup indoors 2.jpg
 
Last edited by a moderator:
The fronius inverters perform well in pvsol, not a whole lot more output but more than Sma and power one with lots of panels.
 
As far as I can see this is not a bad choice. If you check the data sheet the max ac output is 16A which is ideal for a G83/1 install. One important thing to note and something that confused me for a long time is that on the data sheet, where is states max dc input 3200W is not actually the max dc this inverter can handle. Its something to do with a nominal value they have to state for the European market. To find the max amount of dc you can wire to this inverter simply multiply the the max input voltage by the the max input current. In this case its 9,350W (obviously you'd never want to do this). You might think I'm mad but I've spoken to Fronius and SMA about this. Anyway, as I say I'm sure this inverter will be fine and as long as the rest of the installation has been carried out correctly, and on a clear day will give you your 16A output. I'm willing to bet the installers didn't have clearance from the DNO to go above 3.68kW of output anyway????
 

Reply to Have I got the wrong Inverter? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello All, I'm seeking some advice about a solar PV system we had installed in November 2014 please. After 18 months, we seem to be consistently...
Replies
15
Views
6K
crossplot
C
C
Hi all, This is the first on-grid system I design and install. I live in Amman-Jordan but here we follow same UK standards so basically we have...
Replies
7
Views
7K
H
Hi All, I have just had a PV install done on my property this week and reading some of the posts here and the MCS guidlines, etc. I am now a...
Replies
89
Views
16K
Earthstore
E
Many system owners have probably seen changes in the performance of their systems between spring and summer. The days are longer and the sun is...
Replies
16
Views
3K
K
Hi, I have followed this forum now since last autumn and wonder whether some of you experts out there can advise me? I had a system installed last...
Replies
23
Views
3K
Glen Powell
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock