this is baffling.
situation is an existing rfc that has had a minor repair. a socket had been removed and the live cables left in back box and tiled over. cables were pulled back above ceiling and jointed.

prior to reconnectio in a new CU tests were done on the circuit.

now here's the baffling bit:

r1 = 0.28
rN =0.28
r2 = 0.47

fine so far, expected R1+R2 = (0.28 + 0.47) /4 = 0.1875

measured R1+R2 = 0.17 . perfeck.

then, here's the rub....

Rn + R2 = open circuit, tested at 2 points on the ring.

both R1 + R2 and Rn + R2 measured with the respective ends cross connected @ CU.

it's as if the N's are continuous but loose in the sockets but sockets were working fine before.

tester plug lead checked as OK by plugging in a socket on another circuit and live readings were normal.

as i said, a head scratcher.
 
this is baffling.
situation is an existing rfc that has had a minor repair. a socket had been removed and the live cables left in back box and tiled over. cables were pulled back above ceiling and jointed.

prior to reconnectio in a new CU tests were done on the circuit.

now here's the baffling bit:

r1 = 0.28
rN =0.28
r2 = 0.47

fine so far, expected R1+R2 = (0.28 + 0.47) /4 = 0.1875

measured R1+R2 = 0.17 . perfeck.

then, here's the rub....

Rn + R2 = open circuit, tested at 2 points on the ring.

both R1 + R2 and Rn + R2 measured with the respective ends cross connected @ CU.

it's as if the N's are continuous but loose in the sockets but sockets were working fine before.

tester plug lead checked as OK by plugging in a socket on another circuit and live readings were normal.

as i said, a head scratcher.
Can you get access to the joint you mentioned?
 
Figure of eight ring? The "ring" nearest the cu is sound, the rn in the other part of the figure of eight is incomplete. Try measuring r1, rn, r2 from behind the sockets where you're getting odd results.
 
You only have to have neutrals twisted together and then put loosely in the terminal for the connection to be somewhat variable, I would usually expect high resistance rather than open circuit though, especially as the sockets were working.
However any small movement of cables such as when they were brought out of the wall may have affected nearby sockets.
 
You only have to have neutrals twisted together and then put loosely in the terminal for the connection to be somewhat variable, I would usually expect high resistance rather than open circuit though, especially as the sockets were working.
However any small movement of cables such as when they were brought out of the wall may have affected nearby sockets.
thought of that, so just for a laugh, tried Rn+R2 with a 500V IR test. came back with 500Meg.
 
Did you test by using the plugtop lead on your tester? Could be plugtop and socket don't quite make contact as well as whatever appliance is normally plugged in there. Have you tested from the back of the offending sockets?
 
this was a problem that another member had me look at. time was limited as it was 4.00pm yesterday and after sorting out the fault on another job ( see new Ring circuit tripping RCD thread), was gasping for a beer and 25 miles back home.
 
Either the customer went round unscrewing sockets whilst the CU was being put in place or the cables have been mixed up and you are measuring the neutrals with the cpc of another circuit.
 
Can you get access to the joint you mentioned?
can do pete, but that's the next thing for Simon to check. i was only there to give him a second opinion and some pointersas to how to proceed. end of the day, we don't usually test N-E continuity. it's just someting he picked up on when trying to get his head round testing.
 
I go with Richard on this one , loose connection in the back of a socket .
In the test from back of the sockets camp.
 
that's what i have told Simon to do. seems like the N connection is not being seen by plug in . strange though it's same at original (1980's ) sockets and also at new added ones.
 
Either the customer went round unscrewing sockets whilst the CU was being put in place or the cables have been mixed up and you are measuring the neutrals with the cpc of another circuit.
no customer. flat is empty, undergoing refurb. apart from the o/c Rn+R2. all other dead tests are perfect.
 
You wanna be careful Tel, some members might suggest (not me) that your out of your depth, and should get someone in who knows what they're doing :)

I just say that 'cos it just shows, none of us are connoisseurs of the lecky art, and how useful this forum is.
 
i been out of my depth for ages , swimming against the tide of 'er indoors, her ma and her daughter. all seem to think i have a magic wand. fix anything from a leaking roof to a broken karzi. all the while while jabbering over what happened in last night's episode of emmeroids or which starstruck wannabee screecher will win the pox factor.
 
Feel free to hurl abuse my way if you think my next question is demeaning Tel, but.

Did you swap the neutral plug at the tester with the earth plug before testing?
no. tester with plug lead still attached was plugged into a socket on another circuit. L-N 240V. L-e 240V. N-E 0v.
 

Reply to Head Scratcher Time. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
843
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
972
Looking at the EICR form. GENERIC SCHEDULE OF TEST RESULTS Looking for clarification on R1,R2,Rn versus r1,r2,rn continuity values. I have...
Replies
9
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock