Discuss Heating wiring problem. in the Central Heating Systems area at ElectriciansForums.net

Reaction score
16
Does anyone know how I can resolve the following problem .

-Two rooms are fitted with plumbed underfloor heating.
-Room one has own thermstat wired to call 4 wire Actuator on manifold.
-Room two also has own themostat wired to call seperate 4 wire actuator on
manifold.
-Second switch wire on both actuators linked to call pump and zone valve.
-Zone valve then calls boiler.

Problem is that when one thermstat calls its own actuator this back feeds on second switch wire to other actuator.

How can I seperate them in a way that they both can still call the one zone valve ?? :confused:
 
You need 2 relays....energise each with one of the 2 actuator switch wires.On the N/O contacts of the 2 relays link a perm live to one side of each, and link the other side of each to the zone valve.
 
Last edited by a moderator:
What voltage is the system? as obviously you need to make sure the coil is suitable for the job...

I'm guessing 230v from your post if it's operating the zone valve
 
Last edited by a moderator:
Any decent wholesaler will stock them....mount them in a suitable adaptable box on a bit of din-rail....They come in two parts,the base which you wire to,and the relay which just plugs into the base.
Dont be frightened by the number of terminals. There are two coil terminals, and two or more sets of two way contacts..(Common,normally open and normally closed)...common- normally open contacts close when the coil is energised.
 
Last edited by a moderator:
Thanks. Just another quick question.
If supply to FCU in 2.5 t/e I assume ok to use 1.5t/e and 1.5 3c+e for connecting to thermostats,zone valves and 3c+e back to boiler for L,N,E and SW.

Boiler about 6m from UFH manifold so FCU at manifold and 3 pole isolator on the 3c+e at the boiler
 

Reply to Heating wiring problem. in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Up until now I have steered clear of heating systems. I now have quite a bit of work with a builder and will be expected to deal with the...
Replies
4
Views
827
Replacing 15 year old FAR Italian manifolds (2 downstairs, 1 up) with new Warmup units. However, old actuators have 4 core and new only have 2...
Replies
3
Views
922
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
651
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
Hi all, I've noticed that my UFH pump is not always turning on as soon as the stat & valve calls for heat. This results in hot water passing...
Replies
8
Views
607

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock