Discuss Help needed with connecting pendant in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Edij

-
Reaction score
1
Hello ,

I need to connect my lightning pendant and i need some advise.
I have total 3 cables coming out from the calling ,so total3 L 3 N and 3earth.
But how do i connect them correctly? There is only 2 spots for N and 1 more spot for L ,but i got 3 cables for each ? whats does 3 spots in middle for loop suppose to be for?Can i connect all L and all N together in 1 spot?

View attachment 44198

IMG_1476.jpg
 
one of the blacks should be red sleeved. post a pic.of the existing wiring before you disconnect anything. arggh, just seen it.

1. those cpc's (earths) need redoing. bare copper showing.
2. the 3 reds go in the 3 loop terminals.
3. 2 of the blacks are N's. 1 is switched L.

get them wrongand you will have:

a) a burnt out switch
b) a maybe damaged MCB, or a blown fuse.

20 minute job or a sparks. call one.
 
One of the blacks shpuld have had a bit of red sleeving or tape on as its the return from the switch... Also is there an earth fly lead to the cobduit box? Not evident on pics
 
one of the blacks should be red sleeved. post a pic.of the existing wiring before you disconnect anything. arggh, just seen it.

1. those cpc's (earths) need redoing. bare copper showing.
2. the 3 reds go in the 3 loop terminals.
3. 2 of the blacks are N's. 1 is switched L.

get them wrongand you will have:

a) a burnt out switch
b) a maybe damaged MCB, or a blown fuse.

20 minute job or a sparks. call one.

I see ,thank you. I guess i wont touch anything and just call certificated electrician to do it ,dont want to take any risks.
 
Last edited:
take murdoch's mid point as a guide. if it's more you'll need to dig deeper. if less then you can have a couple of beers.
 

Reply to Help needed with connecting pendant in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
421
I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Replies
2
Views
508
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
653
M
Hi Guys I purchased some of the above online around 3 weeks ago, They are a fairly new product, very usefull as you can change both colour from...
Replies
1
Views
303
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
599

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock