Old properties often have earth's from random sockets to the incoming water ....
Discuss Help! Never seen this before! in the UK Electrical Forum area at ElectriciansForums.net
As I can’t find an Earth would you suggest earth rod? Although this zs at db reading is so lowOld properties often have earth's from random sockets to the incoming water ....
just tried that and it wouldn’t pick an Earth up from the casingThat is a lead sheathed cable coming in which should be connected to the ISCO sealing chamber and other ISCO boxes.
Inspect and test the cover of the sealing chamber to see if it is connected to the lead sheath and then test it to see if it gives a good Ze.
Just t
just tried that and it wouldn’t pick an Earth up from the casing
DNO coming on a slow boat from China? that lead time is a disgrace.DNO don’t seem to care! They bassicly told me to put it on a TT system. They can send someone out to see if it can be changed to PME but that’s a 5 week waiting time.
Still waiting for that pic....What about a pic of the main earth terminal in the cu.
wayayy too technical as it's way past beer o'clock.A pic of the gubbins in the CU might help!
Yeah whats's apnin OP get a grip will youStill waiting for that pic....
Keep up Mate pleaseNot sure if anyone has thought of it, but we could do with photos.
DNO don’t seem to care! They bassicly told me to put it on a TT system. They can send someone out to see if it can be changed to PME but that’s a 5 week waiting time.