Hi,
I'd like some help please on installing a zanussi
oven.
The oven manual states "Connection should be via an
Oven Control Circuit. Min size cable 2.5 mm2. Cable
PVC twin & earth. Fuse 15 A min 20 A max.
The total load rating of the oven is 2.48 Kw."
The label on the side of the oven states Max power is
2 790 Kw.
I checked the circuit breaker for the cooker in the
consumer unit and it is a 32 Amp. The old oven is
wired through 13a fused spur socket on the wall, but
uses a 1.5 mm2 cable.
To instal the new oven should I just replace the
1.5 mm2 cable with 2.5 mm2 wired through the 13 a
fused spur socket ?
Thanks