So I’ve finished a rewire recently and I’ve come to testing the ring circuit for the down stairs sockets and I’m not getting what I’m testing in regards to the calculation
LL: 0.36
NN:0.36
EE:0.60(there abouts)
Now when I’m doing the r1+r2 crossing the opposite live and earths but the calculation for obtaining it isn’t what I’m getting when recording the results.
So 0.36+0.36/4= 0.18
But when testing at the sockets I’m getting readings of 0.30 ohms. I’m going to try another calibrated tester this weekend.
Any advice would be appreciated
Thanks